[RE-wrenches] Trojan IND9-6V settings with Outback FX and Flexmax 60
jay peltz
jay at asis.com
Thu Feb 20 15:33:49 PST 2014
HI Larry,
Yep totally confusing about their overview information, and they are working on it to get it more clear.
The specific spec sheets are accurate though.
jay
On Feb 20, 2014, at 3:49 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
> Hey Jay,
>
> What do you have that is different than what I said? Attached is the IND9 data sheet. It shows 2.35 to 2.45 for absorb. I was pointing out that there is confusion: Trojan has multiple publications with different numbers on them.
>
> Larry
> <Screen Shot 2014-02-20 at 1.52.07 PM.png>
>
>
> On Feb 20, 2014, at 9:46 AM, jay peltz <jay at asis.com> wrote:
>
> HI Larry,
>
> I was very curious about your charge specs as they didn't agree with what I have.
> I have contacted Trojan and the specs you show below are for their "signature" line and not the IND line.
>
> The official word on max C rate is 10-13% of max battery capacity for IND line.
> The vpc voltages are in their IND product literature.
>
> jay
>
> peltz power
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140220/32821a23/attachment-0004.html>
More information about the RE-wrenches
mailing list