[RE-wrenches] Battery venting issue
Ray Walters
ray at solarray.com
Wed Feb 5 19:21:17 PST 2014
I can give you one example for them to consider: UPS systems. They all
use sealed VRLA batteries, and are not vented to the outside.
2nd thing for them to chew on: The Midnite Battery boxes are ETL
listed, and you are installing them to the manufacturer's recommendations.
3rd, your use of article 480 is a well worded defense. You should
convert that to a white paper on the subject! What code section are
they using to justify this?
I agree, you can't allow this precedent to be established. I think you
need some backing from SEIA for instance. If they're going to try and
buck decades of established national practice, they really need to have
a darn good reason, and be ready for a challenge.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 2/5/2014 7:38 PM, Allan Sindelar wrote:
> Wrenches,
> I need a bit of help here if you have it. Since 2002 we have installed
> somewhere between 30 and 35 systems with sealed batteries installed in
> manufactured enclosures, originally Outback enclosures and in recent
> years Midnite MNBE enclosures. At least ten of these have been indoors
> in one form or another - usually a laundry or mechanical room. Our
> battery of choice is Concorde SunXtender. We have only added
> mechanical ventilation (Zephyr Power-Vent to outside) if the battery
> enclosure itself is sealed. Nearly all of these have been permitted
> and inspected systems, and we have never had a problem with the
> inspectors. Of course, we always vent flooded systems to the outside,
> nearly always using a Power Vent fan.
>
> Now we have. An AHJ failed a system for lack of ventilation, and our
> attempts to resolve it have not been effective. The Chief Electrical
> Inspector has weighed in, and we are right at the point of filing a
> Request for Code Interpretation with the New Mexico Electrical
> Division Technical Advisory Panel.
>
> I have not wanted to just add ventilation to pass inspection because
> of the precedent doing so is likely to set for future installations.
> The GC on the job supports my attempts to push back, as do the
> homeowners. The Chief Inspector thinks that the 700 square foot
> unheated room in which our system is installed is a bedroom; it's
> actually a storeroom for the homeowners' collectible book home business.
>
> My request: please send me documented work by others establishing that
> PV systems with sealed VRLA batteries are used specifically because
> they are considered safe without venting to the outside. If you know
> of good online links, I could use them too. For example, the AHJ asked
> for a document stating that the batteries or the enclosure were
> specifically approved for this use in an indoor location. I can't -
> Midnite battery enclosures are simply listed to UL508A, which is
> "industrial control panels" and there's nothing specific to this
> application in the standard.
>
> To me this is a common-sense issue, but common sense doesn't cut it
> when needing to prove a procedure. Can anyone help?
>
> For what it's worth, or for those Wrenches with too much spare time,
> below is the text of the original defense of our installation that I
> sent to the AHJ. His response was that he's not an electrical engineer
> and this would have to be taken upstairs. For what it's worth, I'm not
> an EE either... My frustration is showing, I'm sure.
>
> Thank you for any links, reports or other resources you may be able to
> send my way.
> Allan
>
>
> -------- Original Message --------
>
> Mr. [AHJ],
> I have done some research as followup to our discussion last week
> about battery venting for the [X] job. Here are several perspectives
> on the issue:
>
> The NEC Section 480.9(A) states only that "Provisions shall be made
> for sufficient diffusion and ventilation of the gases from the battery
> to prevent the accumulation of an explosive mixture". At root, you are
> questioning whether ventilation of the batteries into the storeroom at
> the [X] home is sufficient under worst-case conditions.
>
> The NEC Handbook entries for Section 480.9(A), which are considered as
> explanatory support documentation and are not Code requirements,
> include two paragraphs that are fundamentally contradictory to each
> other. The two read:
>
> The intent of 480.9(A) is not to mandate mechanical ventilation.
> Hydrogen disperses rapidly and requires little air movement to
> prevent accumulation. Unrestricted natural air movement in the
> vicinity of the battery, together with normal air changes for
> occupied spaces or heat removal, normally is sufficient. If the
> space is confined, mechanical ventilation may be required in the
> vicinity of the battery.
>
> This paragraph refers to batteries in general, including flooded
> batteries which release hydrogen gas as a normal part of the charging
> process. The Handbook section goes on to specifically identify sealed
> batteries as being unlikely to release explosive gases:
>
> Although valve-regulated batteries are often referred to as
> "sealed," they actually emit very small quantities of hydrogen gas
> under normal operation and are capable of liberating large
> quantities of explosive gases if overcharged. These batteries
> therefore require the same amount of ventilation as their vented
> counterparts."
>
> Well, no, not exactly. Valve-regulated batteries may indeed require
> the same amount of ventilation, but not for the same purpose or under
> the same conditions.
>
> Flooded batteries release hydrogen gas as a normal part of every
> charge cycle. While it is unlikely that the hydrogen gas could
> accumulate to the 4% concentration to become combustible, given its
> natural dispersion, the hydrogen sulfide released with the hydrogen
> gas is an unpleasant irritant and is potentially toxic with prolonged
> exposure at high concentrations. Because of the normal gassing during
> the charge cycle, we always provide ventilation of these gases to the
> outside. With sealed batteries, the purpose and intent of ventilation
> is not to ensure ventilation during the normal charge cycle, but
> rather to ensure the safety of the dwelling and its occupants in the
> event of a catastrophic failure resulting in the "worst-case scenario"
> of unregulated overcharge. In actual experience, the charge regulator
> (from the PV array) and the inverter/charger (from a backup generator
> in an off grid home) are the bottlenecks through which all charge
> current must pass, and failures invariably occur in an "open circuit"
> mode, rather than in a "closed circuit without charge regulation" mode.
>
> Nevertheless, we must accommodate the most hazardous potential
> outcome, which would be /unregulated overcharge/ of an /already full
> battery/ during periods of /high insolation/ (or the equivalent input
> from an engine generator). In order to determine the expected amount
> of hydrogen gassing under worst-case conditions, I contacted my
> Concorde distibutor,Marc Kurth ofCentex Batteries, LLC inBastrop, TX,
> 512 308-9002. He in turn spoke with the engineering department at
> Concorde Battery, the manufacturer of the batteries used in the [X] PV
> installation. Their analysis of calculated gassing and airflow rates
> is in the attached pdf document which they provided to us. The
> batteries in the [X] PV system are Concorde SunXtender PVX-9150T,
> rated 915 amp-hours at the C/24 rate. There are 12 cells in a single
> series string of 24 Vnom.
>
> The storeroom in which the PV system is located has interior
> dimensions of 19' by 37' by an average of 10' tall, or approximately
> 7,000 cubic feet. It's a large open space. The room has four Pella
> double-hung windows, each rated by the manufacturer at 0.3 cfm
> fenestration, or 1.2 cfm for all four. Each exterior door (the third
> door to the interior living space is excluded as a conservative
> calculation but also adds to overall ventilation) is rated at 0.6 cfm,
> for a total of 1.2 cfm for the two doors and 2.4 cfm for the building,
> assuming no other openings of any sort, such as for wires or for
> natural convective losses due to any other air leakage or roof
> ventilation.
>
> The 2,000 watt PV array will provide at most about 65 peak amperes of
> DC current into the batteries, for the equivalent of a cumulative
> daily total of around seven hours in summer. (The inverter/charger is
> capable of feeding 105 amperes into the batteries from a generator,
> but by the specific stated preference of the homeowners, the home does
> not have a backup generator and does not include the ability to accept
> generator AC input.) Assuming the worst case of 75 amperes flowing
> unregulated into this 900 ampere-hour battery, this C/12 charge rate
> is capable of raising the batteries to 30 V DC, or 2.50 volts per cell
> (vpc). The cell voltage will not rise about this level because the
> internal resistance of the battery, which increases as the voltage
> increases, prevents it. Note also that 75 amperes is a peak current
> that could only be maintained at midday during conditions of cold, dry
> air when the solar insolation intensity is well above standard test
> conditions (STC) of 1,000 watts/square meter, when the sun is
> perpendicular to the array. As the sun passes across the sky, the
> available output current drops substantially. At a reduced input
> current, the maximum vpc drops to around 2.40 vpc (and continues to
> drop thereafter) and the maximum temperature also drops, in which case
> gassing reduces by a factor of about 20 below the rate at 2.50 vpc.
>
> As an additional factor in our calculations, note that all modern
> charge controllers are designed to receive PV input at a higher
> voltage and lower current than the nominal battery voltage, converting
> this to higher current at the lower actual battery voltage. The
> Midnite Classic charge controller in this application works this way.
> In a closed-circuit failure of the charge controller's functions, the
> higher array voltage and lower current would pass through to the
> batteries. As long as the input voltage is higher than the battery
> voltage, the batteries will accept current, but additional voltage
> does not increase the current into the batteries or the amount of
> hydrogen released. Rather, in this case the PV modules, which are
> wired as four strings of two modules each, will not exceed the rated
> short-circuit of the modules x 1.25 (per NEC for PV source circuits.
> With four strings, this is (8.61 x 4 x 1.25 =) 43.05 amperes. This is
> less than half of the maximum input current used to calculate
> worst-case input (as shown in the following paragraphs), and as such
> is unlikely to be sufficient to raise the cell voltage to even the
> level calculated.
>
> Per the attached engineering analysis by Concorde, assuming that at a
> sustained 2.50 vpc the temperature of the batteries rises to 50ºC
> (122ºF), the amount of hydrogen released at a constant current at 30V
> DC, or 2.50 vpc, at 50ºC is 5.6 cc/hour/Ah/cell. This converts to (5.6
> x 915 x 12 =) 61,488 cc of hydrogen released per hour. Converting
> cubic centimeters to the more useful cubic feet, 61,488/21,317 cc/cuft
> = 2.17 cubic feet per hour of gas released. This amount is less than
> the total fenestration of that room (not including the door to the
> living space) of 2.4 cubic feet per minute, or (2.4 x 60 =) 144 cubic
> feet per hour of natural leakage to the outside through closed windows
> and doors.
>
> To take this one step further, 2.17 cubic feet is 0.031% of the volume
> of the storeroom. It would take 30 times this concentration to exceed
> 1% by volume in an airtight container. 4.1% concentration is the
> threshold at which hydrogen gas becomes combustible.
>
> Also at 2.50 vpc, at 50ºC, the airflow required to keep hydrogen
> accumulation below 1% is 0.0093 liter/minute/Ah/cell, or [(0.0093 x
> 915 x 12)/28.32 liters/cubic foot =] 3.6 cfm, or 216 cubic feet/hour.
> While this exceeds the default window and door fenestration of 144
> cubic feet per hour, it is sufficient to disperse hydrogen. Note that
> these batteries are not in a confined space; the batteries are located
> in a space of 7,000 cubic feet. Note also that is the threshold for
> staying below 1% hydrogen concentration; 4.1% is the threshold at
> which hydrogen becomes explosive.
>
> I reviewed our records pertaining to the use of sealed batteries in
> residential off grid PV systems and in grid-tied PV systems with
> battery backup. We have installed more than thirty such systems,
> although the great majority have been installed since 2005. Of those,
> I have identified at least nine permitted and inspected systems in
> which the batteries have been located in what may be considered
> enclosed spaces without ventilation between the interior space and the
> outside air. Indeed, several of these are in spaces much smaller that
> the Shutt storeroom. This is the first time in which an AHJ has
> expressed concern about adequate ventilation of sealed batteries.
>
> In two of these thirty-plus confined interior installations, the
> sealed batteries were installed in custom-made sealed enclosures which
> were wrapped in sheet plywood with controlled intake ventilation. In
> both of these we purposely installed Power Vent battery fans (as we
> install in all of our systems with flooded lead-acid batteries) ducted
> to the outside as a safety feature to prevent the possibility of
> accumulation of gases within the battery enclosure itself. However, in
> all of the remaining systems we have used manufactured steel battery
> enclosures Listed to UL508A. Ventilation from the cabinet into the
> room where it can dissipate has always been considered to be adequate
> in these applications.
>
> I believe that I have conclusively established that in a worst-case
> scenario, the batteries cannot release enough hydrogen to come even
> close to dangerous levels. In practical terms, if a failure were to
> occur when the residents were away, the batteries would be permanently
> damaged by a failed controller, but no danger exists to the home. If
> the residents are present when the failure occurs, they would in short
> order smell the "rotten egg" smell of hydrogen sulfide. Following
> their noses, they'd find a much stronger smell in the storeroom,
> suspect that the batteries were the source, turn off the circuit
> breakers on the system (which are readily accessible per NEC) and open
> the doors or windows.
>
> The 2011 NEC Hanbook states, as noted above: "If the space is
> confined, mechanical ventilation may be required in the vicinity of
> the battery." The storeroom at the [X] residence is simply not a
> "confined space" as built.
>
> Thank you for your consideration of this defense of our installation
> practices.
> Allan Sindelar
> --
>
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder, *Positive Energy, Inc.*
>
> A Certified B Corporation^TM
> 3209 Richards Lane
> Santa Fe, New Mexico 87507
> *505 424-1112 office 780-2738 cell*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140205/4d0a9263/attachment-0004.html>
More information about the RE-wrenches
mailing list