    <div class="moz-cite-prefix">I can give you one example for them to
      consider:  UPS systems.  They all use sealed VRLA batteries, and
      are not vented to the outside.<br>
      2nd thing for them to chew on:  The Midnite Battery boxes are ETL
      listed, and you are installing them to the manufacturer's
      recommendations.<br>
      3rd, your use of article 480 is a well worded defense.  You should
      convert that to a white paper on the subject!  What code section
      are they using to justify this?  <br>
      <br>
      I agree, you can't allow this precedent to be established.  I
      think you need some backing from SEIA for instance.  If they're
      going to try and buck decades of established national practice,
      they really need to have a darn good reason, and be ready for a
      challenge.<br>
      <br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 2/5/2014 7:38 PM, Allan Sindelar wrote:<br>
    </div>
    <blockquote cite="mid:52F2F599.4020008@positiveenergysolar.com"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      Wrenches,<br>
      I need a bit of help here if you have it. Since 2002 we have
      installed somewhere between 30 and 35 systems with sealed
      batteries installed in manufactured enclosures, originally Outback
      enclosures and in recent years Midnite MNBE enclosures. At least
      ten of these have been indoors in one form or another - usually a
      laundry or mechanical room. Our battery of choice is Concorde
      SunXtender. We have only added mechanical ventilation (Zephyr
      Power-Vent to outside) if the battery enclosure itself is sealed.
      Nearly all of these have been permitted and inspected systems, and
      we have never had a problem with the inspectors. Of course, we
      always vent flooded systems to the outside, nearly always using a
      Power Vent fan.<br>
      <br>
      Now we have. An AHJ failed a system for lack of ventilation, and
      our attempts to resolve it have not been effective. The Chief
      Electrical Inspector has weighed in, and we are right at the point
      of filing a Request for Code Interpretation with the New Mexico
      Electrical Division Technical Advisory Panel. <br>
      <br>
      I have not wanted to just add ventilation to pass inspection
      because of the precedent doing so is likely to set for future
      installations. The GC on the job supports my attempts to push
      back, as do the homeowners. The Chief Inspector thinks that the
      700 square foot unheated room in which our system is installed is
      a bedroom; it's actually a storeroom for the homeowners'
      collectible book home business.<br>
      <br>
      My request: please send me documented work by others establishing
      that PV systems with sealed VRLA batteries are used specifically
      because they are considered safe without venting to the outside.
      If you know of good online links, I could use them too. For
      example, the AHJ asked for a document stating that the batteries
      or the enclosure were specifically approved for this use in an
      indoor location. I can't - Midnite battery enclosures are simply
      listed to UL508A, which is "industrial control panels" and there's
      nothing specific to this application in the standard.<br>
      <br>
      To me this is a common-sense issue, but common sense doesn't cut
      it when needing to prove a procedure. Can anyone help?<br>
      <br>
      For what it's worth, or for those Wrenches with too much spare
      time, below is the text of the original defense of our
      installation that I sent to the AHJ. His response was that he's
      not an electrical engineer and this would have to be taken
      upstairs. For what it's worth, I'm not an EE either... My
      frustration is showing, I'm sure.<br>
      <br>
      Thank you for any links, reports or other resources you may be
      able to send my way.<br>
      Allan<br>
      <div class="moz-forward-container"><br>
        <br>
        -------- Original Message --------<br>
        <br>
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        Mr. [AHJ],<br>
        I have done some research as followup to our discussion last
        week about battery venting for the [X] job. Here are several
        perspectives on the issue:<br>
        <br>
        The NEC Section 480.9(A) states only that "Provisions shall be
        made for sufficient diffusion and ventilation of the gases from
        the battery to prevent the accumulation of an explosive
        mixture". At root, you are questioning whether ventilation of
        the batteries into the storeroom at the [X] home is sufficient
        under worst-case conditions.<br>
        <br>
        The NEC Handbook entries for Section 480.9(A), which are
        considered as explanatory support documentation and are not Code
        requirements, include two paragraphs that are fundamentally
        contradictory to each other. The two read: <br>
        <blockquote> The intent of 480.9(A) is not to mandate mechanical
          ventilation. Hydrogen disperses rapidly and requires little
          air movement to prevent accumulation. Unrestricted natural air
          movement in the vicinity of the battery, together with normal
          air changes for occupied spaces or heat removal, normally is
          sufficient. If the space is confined, mechanical ventilation
          may be required in the vicinity of the battery.<br>
        </blockquote>
        This paragraph refers to batteries in general, including flooded
        batteries which release hydrogen gas as a normal part of the
        charging process. The Handbook section goes on to specifically
        identify sealed batteries as being unlikely to release explosive
        gases:<br>
        <blockquote>Although valve-regulated batteries are often
          referred to as "sealed," they actually emit very small
          quantities of hydrogen gas under normal operation and are
          capable of liberating large quantities of explosive gases if
          overcharged. These batteries therefore require the same amount
          of ventilation as their vented counterparts."<br>
        </blockquote>
        Well, no, not exactly. Valve-regulated batteries may indeed
        require the same amount of ventilation, but not for the same
        purpose or under the same conditions. <br>
        <br>
        Flooded batteries release hydrogen gas as a normal part of every
        charge cycle. While it is unlikely that the hydrogen gas could
        accumulate to the 4% concentration to become combustible, given
        its natural dispersion, the hydrogen sulfide released with the
        hydrogen gas is an unpleasant irritant and is potentially toxic
        with prolonged exposure at high concentrations. Because of the
        normal gassing during the charge cycle, we always provide
        ventilation of these gases to the outside. With sealed
        batteries, the purpose and intent of ventilation is not to
        ensure ventilation during the normal charge cycle, but rather to
        ensure the safety of the dwelling and its occupants in the event
        of a catastrophic failure resulting in the "worst-case scenario"
        of unregulated overcharge. In actual experience, the charge
        regulator (from the PV array) and the inverter/charger (from a
        backup generator in an off grid home) are the bottlenecks
        through which all charge current must pass, and failures
        invariably occur in an "open circuit" mode, rather than in a
        "closed circuit without charge regulation" mode.<br>
        <br>
        Nevertheless, we must accommodate the most hazardous potential
        outcome, which would be <i>unregulated overcharge</i> of an <i>already



          full battery</i> during periods of <i>high insolation</i> (or
        the equivalent input from an engine generator). In order to
        determine the expected amount of hydrogen gassing under
        worst-case conditions, I contacted my Concorde distibutor<font
          face="Times New Roman, Times, serif">,<span style="font-size:
            11pt; color: black;"> Marc Kurth of</span><span
            style="font-size: 11pt; color: black;"> Centex Batteries,
            LLC in</span><span style="font-size: 11pt; color: black;"></span><span
            style="font-size: 11pt; color: black;"> Bastrop, TX, </span><span
            style="font-size: 11pt; color: black;">512 308-9002. He in
            turn spoke with </span>th</font>e engineering department at
        Concorde Battery, the manufacturer of the batteries used in the
        [X] PV installation. Their analysis of calculated gassing and
        airflow rates is in the attached pdf document which they
        provided to us. The batteries in the [X] PV system are Concorde
        SunXtender PVX-9150T, rated 915 amp-hours at the C/24 rate.
        There are 12 cells in a single series string of 24 Vnom.<br>
        <br>
        The storeroom in which the PV system is located has interior
        dimensions of 19' by 37' by an average of 10' tall, or
        approximately 7,000 cubic feet. It's a large open space. The
        room has four Pella double-hung windows, each rated by the
        manufacturer at 0.3 cfm fenestration, or 1.2 cfm for all four.
        Each exterior door (the third door to the interior living space
        is excluded as a conservative calculation but also adds to
        overall ventilation) is rated at 0.6 cfm, for a total of 1.2 cfm
        for the two doors and 2.4 cfm for the building, assuming no
        other openings of any sort, such as for wires or for natural
        convective losses due to any other air leakage or roof
        ventilation. <br>
        <br>
        The 2,000 watt PV array will provide at most about 65 peak
        amperes of DC current into the batteries, for the equivalent of
        a cumulative daily total of around seven hours in summer. (The
        inverter/charger is capable of feeding 105 amperes into the
        batteries from a generator, but by the specific stated
        preference of the homeowners, the home does not have a backup
        generator and does not include the ability to accept generator
        AC input.) Assuming the worst case of 75 amperes flowing
        unregulated into this 900 ampere-hour battery, this C/12 charge
        rate is capable of raising the batteries to 30 V DC, or 2.50
        volts per cell (vpc). The cell voltage will not rise about this
        level because the internal resistance of the battery, which
        increases as the voltage increases, prevents it. Note also that
        75 amperes is a peak current that could only be maintained at
        midday during conditions of cold, dry air when the solar
        insolation intensity is well above standard test conditions
        (STC) of 1,000 watts/square meter, when the sun is perpendicular
        to the array. As the sun passes across the sky, the available
        output current drops substantially. At a reduced input current,
        the maximum vpc drops to around 2.40 vpc (and continues to drop
        thereafter) and the maximum temperature also drops, in which
        case gassing reduces by a factor of about 20 below the rate at
        2.50 vpc.<br>
        <br>
        As an additional factor in our calculations, note that all
        modern charge controllers are designed to receive PV input at a
        higher voltage and lower current than the nominal battery
        voltage, converting this to higher current at the lower actual
        battery voltage. The Midnite Classic charge controller in this
        application works this way. In a closed-circuit failure of the
        charge controller's functions, the higher array voltage and
        lower current would pass through to the batteries. As long as
        the input voltage is higher than the battery voltage, the
        batteries will accept current, but additional voltage does not
        increase the current into the batteries or the amount of
        hydrogen released. Rather, in this case the PV modules, which
        are wired as four strings of two modules each, will not exceed
        the rated short-circuit of the modules x 1.25 (per NEC for PV
        source circuits. With four strings, this is (8.61 x 4 x 1.25 =)
        43.05 amperes. This is less than half of the maximum input
        current used to calculate worst-case input (as shown in the
        following paragraphs), and as such is unlikely to be sufficient
        to raise the cell voltage to even the level calculated.<br>
        <br>
        Per the attached engineering analysis by Concorde, assuming that
        at a sustained 2.50 vpc the temperature of the batteries rises
        to 50ºC (122ºF), the amount of hydrogen released at a constant
        current at 30V DC, or 2.50 vpc, at 50ºC is 5.6 cc/hour/Ah/cell.
        This converts to (5.6 x 915 x 12 =) 61,488 cc of hydrogen
        released per hour. Converting cubic centimeters to the more
        useful cubic feet, 61,488/21,317 cc/cuft = 2.17 cubic feet per
        hour of gas released. This amount is less than the total
        fenestration of that room (not including the door to the living
        space) of 2.4 cubic feet per minute, or (2.4 x 60 =) 144 cubic
        feet per hour of natural leakage to the outside through closed
        windows and doors. <br>
        <br>
        To take this one step further, 2.17 cubic feet is 0.031% of the
        volume of the storeroom. It would take 30 times this
        concentration to exceed 1% by volume in an airtight container.
        4.1% concentration is the threshold at which hydrogen gas
        becomes combustible.<br>
        <br>
        Also at 2.50 vpc, at 50ºC, the airflow required to keep hydrogen
        accumulation below 1% is 0.0093 liter/minute/Ah/cell, or
        [(0.0093 x 915 x 12)/28.32 liters/cubic foot =] 3.6 cfm, or 216
        cubic feet/hour. While this exceeds the default window and door
        fenestration of 144 cubic feet per hour, it is sufficient to
        disperse hydrogen. Note that these batteries are not in a
        confined space; the batteries are located in a space of 7,000
        cubic feet. Note also that is the threshold for staying below 1%
        hydrogen concentration; 4.1% is the threshold at which hydrogen
        becomes explosive.<br>
        <br>
        I reviewed our records pertaining to the use of sealed batteries
        in residential off grid PV systems and in grid-tied PV systems
        with battery backup. We have installed more than thirty such
        systems, although the great majority have been installed since
        2005. Of those, I have identified at least nine permitted and
        inspected systems in which the batteries have been located in
        what may be considered enclosed spaces without ventilation
        between the interior space and the outside air. Indeed, several
        of these are in spaces much smaller that the Shutt storeroom.
        This is the first time in which an AHJ has expressed concern
        about adequate ventilation of sealed batteries.<br>
        <br>
        In two of these thirty-plus confined interior installations, the
        sealed batteries were installed in custom-made sealed enclosures
        which were wrapped in sheet plywood with controlled intake
        ventilation. In both of these we purposely installed Power Vent
        battery fans (as we install in all of our systems with flooded
        lead-acid batteries) ducted to the outside as a safety feature
        to prevent the possibility of accumulation of gases within the
        battery enclosure itself. However, in all of the remaining
        systems we have used manufactured steel battery enclosures
        Listed to UL508A. Ventilation from the cabinet into the room
        where it can dissipate has always been considered to be adequate
        in these applications.<br>
        <br>
        I believe that I have conclusively established that in a
        worst-case scenario, the batteries cannot release enough
        hydrogen to come even close to dangerous levels. In practical
        terms, if a failure were to occur when the residents were away,
        the batteries would be permanently damaged by a failed
        controller, but no danger exists to the home. If the residents
        are present when the failure occurs, they would in short order
        smell the "rotten egg" smell of hydrogen sulfide. Following
        their noses, they'd find a much stronger smell in the storeroom,
        suspect that the batteries were the source, turn off the circuit
        breakers on the system (which are readily accessible per NEC)
        and open the doors or windows. <br>
        <br>
        The 2011 NEC Hanbook states, as noted above: "If the space is
        confined, mechanical ventilation may be required in the vicinity
        of the battery." The storeroom at the [X] residence is simply
        not a "confined space" as built.<br>
        <br>
        Thank you for your consideration of this defense of our
        installation practices.<br>
        Allan Sindelar<br>
        <div class="moz-signature">-- <br>
          <meta http-equiv="Content-Type" content="text/html;
            charset=ISO-8859-1">
          <meta name="ProgId" content="Word.Document">
          <meta name="Generator" content="Microsoft Word 11">
          <meta name="Originator" content="Microsoft Word 11">
          <link rel="File-List" href="SignatureNew_files/filelist.xml">
          <o:smarttagtype
            namespaceuri="urn:schemas-microsoft-com:office:smarttags"
            name="address"> <o:smarttagtype
              namespaceuri="urn:schemas-microsoft-com:office:smarttags"
              name="PostalCode"> <o:smarttagtype
                namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                name="State"> <o:smarttagtype
                  namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                  name="City"> <o:smarttagtype
                    namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                    name="Street">
                    <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>6</o:Revision>
  <o:TotalTime>2</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-09-23T20:34:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>69</o:Words>
  <o:Characters>394</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>462</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]--><!--[if !mso]><object
 classid="clsid:38481807-CA0E-42D2-BF39-B33AF135CC4D" id=ieooui></object>
<style>
st1\:*{behavior:url(#ieooui) }
</style>
<![endif]-->
                    <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="5122"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
                    <div class="Section1">
                      <p class="MsoNormal"><b>Allan <span
                            class="SpellE">Sindelar</span></b><br>
                        <span style="font-size:10.0pt"><a
                            moz-do-not-send="true"
                            href="mailto:Allan@positiveenergysolar.com"><u><span
                                style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
                        <span style="font-size:10.0pt">NABCEP Certified
                          PV Installation Professional<br>
                          NABCEP Certified Technical Sales Professional<br>
                          New Mexico EE98J Journeyman Electrician<br>
                          Founder, <b>Positive Energy, Inc.<o:p></o:p></b></span></p>
                      <p class="MsoNormal"><span
                          style="font-size:10.0pt">A Certified B <span
                            class="SpellE">Corporation<sup><span
                                style="font-size:7.5pt">TM</span></sup></span><br>
                          <st1:address w:st="on"><st1:street w:st="on">3209


                              Richards Lane</st1:street><br>
                            <st1:city w:st="on">Santa Fe</st1:city>, <st1:state
                              w:st="on">New Mexico</st1:state> <st1:postalcode
                              w:st="on">87507</st1:postalcode></st1:address><br>
                          <b>505 424-1112 office 780-2738 cell</b><br>
                          <a moz-do-not-send="true"
                            href="http://www.positiveenergysolar.com/"
                            target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>
                      <p class="MsoNormal"><span
                          style="font-size:10.0pt"><span
                            style="mso-spacerun:yes"> </span></span></p>
                    </div>
                  </o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></div>
        <br>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>