We have, if there are two separate mains each 200 amps the meter socket is
400 amps just don't overload one side
On Jan 23, 2014 11:31 AM, "John Powell" <abe at solforce.com> wrote:

> Has anyone tried to connect one 40 amp inverter output circuit to each of
> the two breakers on a 2 x 200AMP single meter main panel in California?
>  This would yield 80 amps of solar feed into the panel and the meter using
> two discreet circuits.  It would stay under the 120% rule for each 200 amp
> breaker/buss and the 400 amp buss that serviced the line side of the two
> 200 AMP breakers.
>
> Kosher?
>
>