[RE-wrenches] (RE-wrenches) 2x200 amp meter main panel question

Dave Click daveclick at fsec.ucf.edu
Thu Jan 23 12:53:41 PST 2014


I would think this would be fine, so maybe I am missing the issue. Does 
CA have a state-specific rule on this? What you're asking is whether you 
can safely install a 40A inverter circuit in each of your interior 
[200-225A] panelboards fed from this meter main, right? This is two 
separate load-side interconnections, one per service disconnect.

DKC

On 2014/1/23, 15:30, William wrote:
> John:
>
> These panels are typically rated only 320A continuous duty, so I think your numbers would not compute.
>
> William
>
>> On Jan 23, 2014, at 11:31 AM, John Powell <abe at solforce.com> wrote:
>>
>> Has anyone tried to connect one 40 amp inverter output circuit to each of the two breakers on a 2 x 200AMP single meter main panel in California?
>>