Hi Dan,

I still have 4 Trace U series inverters in the field and have told these customers that they should be saving up for a new inverter for the last 10 years.  Is there some preventive troubleshooting I could do before they potentially have the problem Drake is describing,  or just die of old age?   I have an O scope,  but have never actually used it on Modified Sine Wave....

Thanks,

Jason Lerner
Waldron Power and Light Co.

On May 20, 2014, at 7:54 AM, Exeltech wrote:

> Hello Drake,
> 
> As a professional electrial design engineer in the solar energy industry, I can say without hesitation, the simple answer to your question is "Yes".  Waveforms can deterioriate as components age.  Lower-quality capacitors will dry out in 20 years' use (or less!), and this in turn can indeed alter the waveform.  You'd need at a minimum a good oscilloscope to observe the waveform.  If it's really ragged, and no longer stair-stepped, the inverter is clearly suspect.  If it resembles a "Pyramid", there may be another issue afoot.
> 
> Motors connected to modified square wave power turn at lower RPM and operate [sometimes much] hotter than their sine-fed bretheren.  Over time, the increased heat takes its toll on the wire insulation in the motor, causing an eventual breakdown of the insulation and a short-circuit of the windings.  Presto!  Motor BBQ (sometimes inverter too).
> 
> 
> By the way .. to use "quality" in context with reference to a modified square wave is quite an oxymoron .. but in this case, it fits.
> 
> 
> Dan
> 
> --------------------------------------------
> On Tue, 5/20/14, Drake <drake.chamberlin at redwoodalliance.org> wrote:
> 
> Subject: [RE-wrenches] Modified sine deterioration
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Tuesday, May 20, 2014, 9:24 AM
> 
> Hello Wrenches,
> 
> We are diagnosing a system with a 20 year old Trace DR 1512 inverter. Recently a motor burned out that had been running on the system. I do understand that modified sine (modified square) wave inverters are hard on motors in general.
> 
> My question is, "does the quality of the Mayan Pyramid sine wave deteriorate with time as the capacitors dry up, or for any other reason?  Would the power quality be expected to have declined on an old unit like this?
> 
> Thanks,
> 
> Drake
> 
> Drake Chamberlin
> Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV
> 740-448-7328
> http://athens-electric.com/ 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 




More information about the RE-wrenches mailing list