[RE-wrenches] Busbar 120% rule
Troy Harvey
taharvey at heliocentric.org
Fri Mar 28 13:35:13 PDT 2014
Very interesting.
So, it is not a overcurrent risk, but a heat issue that may lead to a nuisance breaker tripping issue?
On Mar 27, 2014, at 12:46 PM, Dave Click <daveclick at fsec.ucf.edu> wrote:
> I had a nice response all typed up before rediscovering my original source. Simple answer: there's still a thermal load to deal with even though there's no point on the bus seeing a current above the busbar rating. I am a linking machine today:
> http://www.nmsu.edu/~tdi/Photovoltaics/Codes-Stds/690.64(B)(2)Load%20Side%20Connections.pdf
>
> While this situation of connecting supply overcurrent devices at opposite ends may be
> safe for restricted conductors, it may not be suitable for busbars in panel boards, even
> though this allowance is in the 2008 NEC. Panel boards are subject to busbar current
> limitations and are also subject to thermal limitations due to the heating associated with
> the thermal trip elements in the common thermal/magnetic molded case circuit breakers.
> For example a 100-amp, 120/240V panel board is tested during the listing process with a
> 100 amp main breaker and two 100-amp load breakers (one per phase) mounted directly
> below the main breaker. The ambient temperature is raised to 45 degrees Celsius, the
> input and output currents are set at 100 amps, the temperature is allowed to stabilize,
> and the panel must pass this test with no deformation of any parts. If we add a backfed
> PV breaker pair, for example 50 amps, at the bottom of the panel, and if the loads on the
> panel were increased to 150 amps, no breakers would trip, no busbars would be over
> loaded, but the thermal load in the panel would be that associated with 300 amps, not the
> 200 amps the panel was designed and listed for. Panel manufacturers have stated that
> these panels cannot pass UL listing tests with those excessive thermal loads.
>
> On 2014/3/27, 14:34, Troy Harvey wrote:
>> I am wondering about the busbar 120% rule, and if there is any wiggle room in the 2014 NEC.
>>
>> Fundamentally I don't understand the 120% rule. If my solar breaker is installed properly at the bottom of the busbar, and the grid-tie breaker is installed at the top, and the busbar itself is rated for 120% of the panel rating, I don't see any means by which a solar breaker of a size substantially larger than 120% could cause a problem. There can be no place on the busbar under any situation (that I can think of) that would exceed 120% because the supply current is coming from opposite ends of the bus bar - even in the worst case load situation. So even if I had a huge PV system (100A), backfeeding the bottom of a 200A panel, I don't see a situation where there is more than 200A over any one section of busbar. Am I wrong, or is the NEC just too prescriptive for its own good?
>>
>> Also would you say that the 120% is based on the inverter max output or backfeed breaker size?
>>
>>
>> thanks,
>>
>> Troy Harvey
>> ---------------------
>> Principal Engineer
>> Heliocentric
>> 801-453-9434
>> taharvey at heliocentric.org
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140328/5acf7686/attachment-0003.html>
More information about the RE-wrenches
mailing list