[RE-wrenches] AC Combiner with main breaker as system disconnect
Brian Teitelbaum
bteitelbaum at aeesolar.com
Wed Mar 12 14:32:02 PDT 2014
One big omission, in the otherwise fine Soligent white paper, is that the 60A minimum disconnect has to be rated as "Service Equipment". Generally this means a "Heavy-Duty" safety switch or Service-rated load center with Main breaker.
I don't see why an AC breaker panel, with a Main breaker, couldn't act as the PV system disconnect, as long as it's Service-rated, a minimum of 60A, and the utility does not require an external-handle disconnect, lockable in the off position. Many utility companies still do.
Brian Teitelbaum
AEE Solar
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 12, 2014 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Don't utter the word tap. :)
See:
http://www.soligent.net/documents/HappyLandings_v3.pdf
We usually specify a fusible disconnect for overcurrent protection when grouping the PV AC combiner with the main premises disconnect is not practical.
Jason Szumlanski
Fafco Solar
On Wed, Mar 12, 2014 at 1:31 PM, <kevin at renovusenergy.com<mailto:kevin at renovusenergy.com>> wrote:
I am trying to determine whether an AC combiner panel (for multiple inverter outputs) with main breaker can be also used as the PV system disconnect?
This is for a line tap situation. I am accustomed to doing these systems with an AC combiner, and separate enclosure for a breaker style, line tap over current protection.
Any thoughts/comments would be appreciated.
Thanks,
Kevin
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140312/0d6e9071/attachment-0003.html>
More information about the RE-wrenches
mailing list