[RE-wrenches] AC Combiner with main breaker as system disconnect
Jason Szumlanski
jason at fafcosolar.com
Wed Mar 12 14:13:46 PDT 2014
Don't utter the word tap. :)
See:
http://www.soligent.net/documents/HappyLandings_v3.pdf
We usually specify a fusible disconnect for overcurrent protection when
grouping the PV AC combiner with the main premises disconnect is not
practical.
Jason Szumlanski
Fafco Solar
On Wed, Mar 12, 2014 at 1:31 PM, <kevin at renovusenergy.com> wrote:
> I am trying to determine whether an AC combiner panel (for multiple
> inverter outputs) with main breaker can be also used as the PV system
> disconnect?
>
> This is for a line tap situation. I am accustomed to doing these systems
> with an AC combiner, and separate enclosure for a breaker style, line tap
> over current protection.
>
> Any thoughts/comments would be appreciated.
>