[RE-wrenches] Solaredge inverters w/ backup generator
Jerry Shafer
jerrysgarage01 at gmail.com
Thu Feb 13 18:21:11 PST 2014
I have done systems in Hawaii, here is one with a 30 k PV system and with a
250k Cummins back up genny. We have a contactor in the ATS that will open
if the genny is operating, this in turn sends a door open signal to the
Satcon shutting it down I don't want anything effecting the genset
operation so with the open created in the ATS it tricks the inverter to
shut off safely. We as a policy will not run a genset and PV unless as a AC
coupling system and you have some active over voltage like freq and voltage
triggers.
Jerry
On Feb 8, 2014 7:31 AM, "Kirk Herander" <kirk at vtsolar.com> wrote:
> Hello,
>
>
>
> I recently posed the question to Solaredge tech support, wondering if
> their inverter, in this case a 20kw 480 3-phase, would have any issues if
> it were connected to an AC panel backed up by a generator. They told me no
> problem, for the inverter's anti-islanding will work if it sees the
> "generator frequency" and therefore will not try to push PV power to the
> panel. But isn't 60 hz, 60hz regardless of origin? There's got to be more
> to it than that. I question this because I asked the same to SMA several
> years ago and they were hard-set against connecting Sunnyboys to a panel
> with generator backup, so I always would establish the point of
> interconnection upstream of the generator feed. Comments? Thanks.
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140213/00575de5/attachment-0003.html>
More information about the RE-wrenches
mailing list