[RE-wrenches] Trace 2548 intermittent power problem...55 not 25
Eric.Bentsen at schneider-electric.com
Eric.Bentsen at schneider-electric.com
Thu Oct 17 14:07:54 PDT 2013
Hi Eric,
Sounds like a bad control board.
Swap the inverter and you should be back in business.
Rgds,
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
"SunHarvest" <eric at harvesthesun.com>
To:
"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date:
10/17/2013 11:28 AM
Subject:
[RE-wrenches] Trace 2548 intermittent power problem...55 not 25
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
I was looking at a scratch pad note where I wrote 25 instead of 55...Yes,
it is a SW5548. Definitely not set to "Search"...it's in "On" mode. I've
checked error codes. No "Yes" messages. I am wondering about a firmware
upgrade although I have serious doubt that will clear up the problem.
I guess I will try the swap and see if that does the trick.
On the genny, I try to stay away from genset service but I can definitely
check some of the more simple items like check oil & coolant.
Thanks guys.
----- Original Message -----
From: Allan Sindelar
To: RE-wrenches
Sent: Thursday, October 17, 2013 10:36 AM
Subject: Re: [RE-wrenches] Trace 2548 intermittent power problem
Eric,
A Trace 2548 with automatic generator start? I don't believe there ever
was such a thing. I suspect that you're referring to either a SW4048 or
SW5548. If so, your first step is to check the error codes, some of which
are found in Menu Heading 2 (for generator-related issues) and the rest in
Heading 5. Any "Yes" message as you scroll through them is a good hint.
This inverter is at least 13 years in service, likely more. Sounds like a
pre-GTI Y2K system. The units are remarkably robust and reliable, but it
may well have a glitch in the firmware or voltage/frequency sensors. The
extra inverter is your ace in the hole, once you determine what the issue
is.
Allan
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
On 10/17/2013 10:41 AM, SunHarvest wrote:
I have encountered a Trace 2548 in seemingly good working condition. I was
called out to troubleshoot a Grid-tied, battery back-up system with the
following problem:
- Upon loss of grid power there is about a 5 second lapse (no power to
house) before the BB system engages. Power to the critical loads panel
from the Trace is restored after the 5 second lapse.
- After another 5 seconds the Trace will disconnect power to the loads.
This on-off cycle continues until grid power is restored.
After checking voltage & S.G. values, I determined that the 11 year old
batteries needed to be replaced and I assumed this was the cause of the
Trace on-off cycling.
I also found that half of his PV array had bad BP modules. BP replaced all
of the modules under somewhat of a warranty. So, new modules, new
batteries, and a new Outback FM60 charge controller. After all upgrades I
ran through a simulated power outage again and the intermittent power
problem persists!
He also has gen support enabled - connection to an Onan "RV Genset BGE NHE
(??) - and when I start the genny from the inverter, by selecting "On" not
"Auto", the genset fires right up but only stays on for about 30 seconds
before it too shuts off and enters a cycling between auto-starting from
the inverter and shutting down.
This behavior is beyond me. So, I'm seeking help from the pros. Anyone
know what's going on here? The customer has another Trace 2548, unused,
sitting in a box. So, if I needed to I could swap out the inverter and see
if that makes a difference...?
Eric
SunHarvest
(530)798-3738
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131017/fc5c0952/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131017/fc5c0952/attachment-0004.jpe>
More information about the RE-wrenches
mailing list