Eric,
30% of C is high for all flooded batteries I know of. I'd worry about the high temperatures and grid warping. Some AGM's can handle 5C charge without harm.
Larry
On Oct 1, 2013, at 11:10 AM, Eric.Bentsen at schneider-electric.com wrote:
Hi Guys,
Calling for 30% C for max charge current on flooded batt. Pretty aggressive don't you think?
Even more strange is the spec for 2V cells. They call for 20% for flooded but only 15% for gel/AGM? usually gel/agms take HIGHER max charge rate than flooded don't they?
Thanks,
Eric
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site: www.schneider-electric.com/solar | Address: 250 South Vasco Rd., Livermore, CA 94551
<Mail Attachment.jpeg>
*** Please consider the environment before printing this e-mail
<eastpenndeka.zip>_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131001/1c0d6930/attachment-0004.html>
More information about the RE-wrenches
mailing list