William,
Two possibilities:
1) I'd try a GVFX with the genny they have. If the voltage and frequency on the genny are within "grid" parameters and is stable enough, it should work just fine. If not:
2) get a VFX and a GVFX ac board. Maybe save yourself some time by not mounting the VFX on the wall until you change the board when the grid arrives.
Good Luck, Bob-O
On Aug 8, 2013, at 8:47 AM, William Miller wrote:
Friends:
We a have a client that is off-grid right now but will have a grid connection in a few months. They need an inverter that will connect to a generator now and the grid later. Can the Outback G series inverter do that? How about any other inverters in the 4Kw range?
Thanks in advance.
William