<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">William,<div>Two possibilities:</div><div>1) I'd try a GVFX with the genny they have. If the voltage and frequency on the genny are within "grid" parameters and is stable enough, it should work just fine. If not:</div><div>2) get a VFX and a GVFX ac board. Maybe save yourself some time by not mounting the VFX on the wall until you change the board when the grid arrives. </div><div>Good Luck, Bob-O</div><div><br><div><br><div><div>On Aug 8, 2013, at 8:47 AM, William Miller wrote:</div><br class="Apple-interchange-newline">
<meta content="text/html; charset=us-ascii" http-equiv="Content-Type">
<meta name="GENERATOR" content="MSHTML 8.00.6001.23507">
<div>
<div><span class="362444315-08082013"><font face="Arial">Friends:</font></span></div>
<div><span class="362444315-08082013"><font face="Arial"></font></span> </div>
<div><span class="362444315-08082013"><font face="Arial">We a have a client that is
off-grid right now but will have a grid connection in a few months. They
need an inverter that will connect to a generator now and the grid later.
Can the Outback G series inverter do that? How about any other inverters
in the 4Kw range?</font></span></div>
<div><span class="362444315-08082013"><font face="Arial"></font></span> </div>
<div><span class="362444315-08082013"><font face="Arial">Thanks in
advance.</font></span></div>
<div><span class="362444315-08082013"><font face="Arial"></font></span> </div>
<div><span class="362444315-08082013"><font face="Arial">William</font></span></div>
<div><span class="362444315-08082013"><font face="Arial"></font></span> </div>
<div> </div>
<div align="left"><span><Gradient Cap flat.gif></span><br></div>
<div align="left"><font face="Arial">17395 Oak Rd. Atascadero, CA 93422</font></div>
<div align="left"><font face="Arial"><a href="http://www.millersolar.com/">www.millersolar.com</a></font></div>
<div align="left"><font face="Arial">805-438-5600 voice*</font></div>
<div align="left"><font face="Arial">*Note: above number replaces cell
number</font></div>
<div> </div></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Change email address & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div><br></div></div></body></html>