[RE-wrenches] C60 setpoint question
Eric.Bentsen at schneider-electric.com
Eric.Bentsen at schneider-electric.com
Thu Aug 1 14:47:44 PDT 2013
Hi Allen,
The absorption time is actually only 1 hour for the C-series controllers.
Battery manufacturers are always the final authority on
how their batteries should be charged. If they say you can charge at
14.2-14.4V indefinitely, then increase the float setting.
Eric
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Allan Sindelar <allan at positiveenergysolar.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
08/01/2013 01:20 PM
Subject:
[RE-wrenches] C60 setpoint question
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Wrenches,
Eden, our main off grid field tech, came across a situation about which I
want to ask the group for advice, please.
The system: existing old/funky off grid 12V residential system, done by
others over many years; this was our first visit. Owner out of state,
currently rented, owner's complaint is that the old Heart 2800 EMS
inverter is shutting down at times. Six four year old Concorde SunXtender
PVX-3050Ts, so 900 rated amp-hours in three strings at 12V. Approximately
830 watts of a hodgepodge of older modules, but well below rated output at
present, though no obvious failures. Trace C60 charge controller. Our
assessment after a site visit is that the batteries have been chronically
undercharged and are showing signs of premature sulfation.
With AGM batteries such as these, we have been encouraged (by Midnite tech
support and others) to set really long absorption times - we have some
systems with six-hour absorptions. The logic is that theese batteries can
tolerate - indeed thrive on - staying at absorption voltage of 14.2 - 14.4
V (for 12 V nominal) indefinitely, and given the fickle nature of off grid
PV charging, this maximizes the likelihood of their getting full most
days. This logic makes total sense to me.
Most modern MPPT charge controllers have a programmable absorption time,
and some have a done amps (a.k.a. float transition current), to allow them
to transition to float if the charge current necessary to maintain
absorption voltage drops below a set threshold (typically 1-3% of battery
capacity). The C60 has neither, but rather has a nonadjustable two-hour
timed absorption. This brings the question: is there any good reason that
the float voltage on the C60 should not be set to the same voltage as the
bulk/absorption voltage, such that they never drop into float? When
sufficient input is available to get the batteries full, they are just
allowed to stay in absorption mode indefinitely, slowly getting the energy
necessary to reach 100%.
We have installed many Concorde AGM batteries, but never with an old
C-series controller. This idea seems wacky, but the more I think about it,
the more I can't see any problem with it. What do the rest of you advise?
Thanks, Allan
--
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130801/bca81b99/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130801/bca81b99/attachment-0004.jpe>
More information about the RE-wrenches
mailing list