<br><font size=2 face="sans-serif">Hi Allen,</font>
<br><font size=2 face="sans-serif">The absorption time is actually only
1 hour for the C-series controllers.  Battery manufacturers are always
the final authority on </font>
<br><font size=2 face="sans-serif">how their batteries should be charged.
If they say you can charge at 14.2-14.4V indefinitely, then increase the
float setting.</font>
<br><font size=2 face="sans-serif">Eric<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_09C62B1C09C626D400772E7588257BBA></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Allan Sindelar <allan@positiveenergysolar.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">08/01/2013 01:20 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] C60 setpoint question</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Wrenches,<br>
Eden, our main off grid field tech, came across a situation about which
I want to ask the group for advice, please.<br>
<br>
The system: existing old/funky off grid 12V residential system, done by
others over many years; this was our first visit. Owner out of state, currently
rented, owner's complaint is that the old Heart 2800 EMS inverter is shutting
down at times. Six four year old Concorde SunXtender PVX-3050Ts, so 900
rated amp-hours in three strings at 12V. Approximately 830 watts of a hodgepodge
of older modules, but well below rated output at present, though no obvious
failures. Trace C60 charge controller. Our assessment after a site visit
is that the batteries have been chronically undercharged and are showing
signs of premature sulfation.<br>
<br>
With AGM batteries such as these, we have been encouraged (by Midnite tech
support and others) to set really long absorption times - we have some
systems with six-hour absorptions. The logic is that theese batteries can
tolerate - indeed thrive on - staying at absorption voltage of 14.2 - 14.4
V (for 12 V nominal) indefinitely, and given the fickle nature of off grid
PV charging, this maximizes the likelihood of their getting full most days.
This logic makes total sense to me.<br>
<br>
Most modern MPPT charge controllers have a programmable absorption time,
and some have a done amps (a.k.a. float transition current), to allow them
to transition to float if the charge current necessary to maintain absorption
voltage drops below a set threshold (typically 1-3% of battery capacity).
The C60 has neither, but rather has a nonadjustable two-hour timed absorption.
This brings the question: is there any good reason that the float voltage
on the C60 should not be set to the same voltage as the bulk/absorption
voltage, such that they never drop into float? When sufficient input is
available to get the batteries full, they are just allowed to stay in absorption
mode indefinitely, slowly getting the energy necessary to reach 100%.<br>
<br>
We have installed many Concorde AGM batteries, but never with an old C-series
controller. This idea seems wacky, but the more I think about it, the more
I can't see any problem with it. What do the rest of you advise?<br>
Thanks, Allan<br>
</font>
<br><font size=3>-- </font>
<p><font size=3><b>Allan Sindelar</b></font><font size=2 color=blue><u><br>
</u></font><a href=mailto:Allan@positiveenergysolar.com><font size=2 color=#0000a1><u>Allan@positiveenergysolar.com</u></font></a><font size=2><br>
NABCEP Certified PV Installation Professional <br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
Founder and Chief Technology Officer<b><br>
Positive Energy, Inc.</b>, a Certified B Corporation</font><font size=1><sup>TM</sup></font><font size=2><br>
3209 Richards Lane<br>
Santa Fe, New Mexico 87507<b><br>
505 424-1112 office 780-2738 cell</b></font><font size=2 color=blue><u><br>
</u></font><a href=http://www.positiveenergysolar.com/ target=_blank><font size=2 color=blue><u>www.positiveenergysolar.com</u></font></a>
<p><font size=2> </font>
<p><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<p>
<p>