[RE-wrenches] Outback AC coupling Sunpower?
Drake
drake.chamberlin at redwoodalliance.org
Thu Aug 1 07:23:50 PDT 2013
I did AC couple a Magnum inverter to an existing Sunpower
system. It works. The Magnum features frequency shift control, but
recommends the use of a protective relay also.
At 04:59 PM 7/30/2013, you wrote:
>Hi All;
>
>I know AC coupled systems have been covered before, but I have a new
>issue: positive grounding. A customer with an existing 8kw
>Sunpower system wants to add backup. He was put off by the high
>cost the Sunny Island, so I was steering him towards a single
>Outback VFX coupled to just one of his 3 inverters. The issue is
>how will the VFX work with positive grounded inverters. I'm
>assuming that since the two inverters will only be connected by AC,
>that the positive vs negative grounding of their separate DC systems
>will not matter. Any experience with this particular scenario:
>Sunpower system AC coupled to an Outback?
>Also, would I even need a GVFX, since the inverter would only be
>used during outages (which might allow a generator to be used later
>as well) A VFX should still AC couple to the GT inverter during an
>outage, right?
>
>Thanks as always,
>
>--
>R.Ray Walters
>CTO, Solarray, Inc
>Nabcep Certified PV Installer,
>Licensed Master Electrician
>Solar Design Engineer
>303 505-8760
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
More information about the RE-wrenches
mailing list