This has happened to me personally, and to other customers I have dealt
with over the years. In my case, I got my hands
on (4) used Interstate Workaholic L16 batteries. I was unable to achieve
an acceptable SG because the voltage would not
climb above 14V (using 20A charger). I used a clamp-on DC amp meter to
verify a full 20A going into the batteries, but the voltage
would not climb any higher. It was as if energy was being lost within the
batteries. When I separated the bank into sets of two,
the ratio of current-to-capacity was improved and I was able to equalize
the daylights out of them, and eventually recovered
their performance. I have heard of the condition where the battery has low
SOC, and the charger causes the voltage to increase
very quickly, but I cannot definitely attribute that to sulfation. It
sounds more like an internal open circuit condition. I do know it
usually results in the need to replace the batteries.
Rgds
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
jay peltz <jay at asis.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
07/23/2013 07:33 PM
Subject:
Re: [RE-wrenches] Tri-Star MPPT
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Hi Eric,
While agree with most all your assessments,
Can you please elaborate on the "sulfation causes the voltage not to
climb?"
This is quite counter to what I have seen and what the battery people say?
Thanks
Jay
Peltz power
Sent from my iPad
On Jul 23, 2013, at 2:48 PM, Eric.Bentsen at schneider-electric.com wrote:
Hi William,
If the SG was 1.26, of course the battery voltage would increase
quickly to >30V (which is high for warm weather, BTW).
It has been my experience that sulfation causes the voltage NOT to climb.
Especially when you have a very large bank, and a
relatively small amount of solar.
Sometimes it is necessary to reduce the bank size into smaller sets to
equalize them and recover their performance.
This method of reducing bank size is also effective to compare performance
and weed out a potentially bad battery.
Systems that have a lot of capacity, with a relatively small amount of
charge current usually creates problems, because
the load demand exceeds solar production.
This results in batteries that operate with partial SOC, which is when
sulfation is most prevalent. With (8) L16s, you have approx
800Ahrs of capacity (24V bank). It would take significantly more than 8A
of charge current to properly care for a bank that size.
Rgds,
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130724/2fe94f6e/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130724/2fe94f6e/attachment-0004.jpe>
More information about the RE-wrenches
mailing list