[RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

Kirk kirk at vtsolar.com
Mon Jun 17 16:39:20 PDT 2013


The 120% rule applies to both commercial and residential from the 2008 code on.

Kirk Herander
VSE

On Jun 17, 2013, at 2:58 PM, Allan Sindelar <allan at positiveenergysolar.com> wrote:

> Pekka,
> I believe that the 120% rule is only for residential application. Unless it's changed (and I don't do commercial any more, so I may be all wet here) you're limited to 100% on commercial       applications. The assumption is that a commercial service may already be running at or close to full ampacity, while residential is unlikely ever to do so.
> Allan
> 
> Allan Sindelar
> Allan at positiveenergysolar.com
> NABCEP Certified PV Installation Professional 
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> Positive Energy, Inc., a Certified B CorporationTM
> 3209 Richards Lane
> Santa Fe, New Mexico 87507
> 505 424-1112 office 780-2738 cell
> www.positiveenergysolar.com
>  
> On 6/17/2013 11:33 AM, Pekka Laine wrote:
>> Dear Fellow Wrenches,
>> 
>> We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A.  We are landing those into a dedicated load center with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 160A breaker.  This also equals to the maximum we can backfeed into a 800A/800A Main Service on the load side according to the "120%" rule.
>> 
>> The problem now is that we cannot locate any kind of 160A breaker or even a 160A fuse for a AC disconnect.
>> 
>> Has anybody ever done this without doing a "line-side tap?" It is hard to believe that there wouldn't be an existing solution to landing maximum PV into a 800A service. Are we missing something?
>> 
>> Any good ideas or comments would be appreciated.
>> 
>> Sincerely,
>> 
>> Pekka Laine
>> 
>> President
>> Photon Solar Power Inc.
>> www.PhotonSolarPower.com
>> Cell. 760-556-8170
>> Toll Free 888-SUN-ACDC
>> CA Lic. #933648
>> NABCEP Certified PV Installer # 032611-174
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> .
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130617/b828e83f/attachment-0004.html>


More information about the RE-wrenches mailing list