Does the 800A main panel have a main 800A breaker? If not, then couldn't you
install a 175A breaker?
800 x 1.2 = 960A - (main breaker size) = Allowed PV breaker size.
We did a design for a project in Hawaii recently were we connected to a
208Y/120V 800A main panel with a 350A PV breaker.
--
John Stimac | Corvallis, OR
Renewable Energy Associates LLC
541-754-2001 Office/Fax
john at renewableassociates.com
www.renewableassociates.com
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Pekka Laine
Sent: Monday, June 17, 2013 10:34
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service
Dear Fellow Wrenches,
We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters,
each outputting max. 25A. We are landing those into a dedicated load center
with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would
need a 160A breaker. This also equals to the maximum we can backfeed into a
800A/800A Main Service on the load side according to the "120%" rule.
The problem now is that we cannot locate any kind of 160A breaker or even a
160A fuse for a AC disconnect.
Has anybody ever done this without doing a "line-side tap?" It is hard to
believe that there wouldn't be an existing solution to landing maximum PV
into a 800A service. Are we missing something?
Any good ideas or comments would be appreciated.
Sincerely,
Pekka Laine
President
Photon Solar Power Inc.
www.PhotonSolarPower.com
Cell. 760-556-8170
Toll Free 888-SUN-ACDC
CA Lic. #933648
NABCEP Certified PV Installer # 032611-174
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list