David Katz dkatz at aeesolar.com
Sun May 26 11:14:27 PDT 2013


Jeremy
I have a system on my house with 6 kW of grid tie inverters AC coupled to an Outback Radian, which is actually two 4 kW inverters in one box.  It works great in full sun with the grid off. I don't see a problem with what you are doing.
David Katz

Sent from my iPhone

On May 25, 2013, at 6:52 AM, "All Solar" <allsolar at scswifi.net> wrote:

> Hope everyone is enjoying their weekend!
> I have a system where we have Installed a pair of XW inverters along with a 10k Fronius inverter. 
> We have been told that we need to limit the PV watts to the lowest XW inverter. We have XW capacity in excess of the array, so why can't they entire array feed the system when the grid is down?
> Of course tech support is tougher when you use different brand names, but I'm sure this has been done in the field already.
> Please contact me off list If you can help us out. The customers electrician on this job has been trying hard to figure it out, but I think he might be in too deep!
> 
> Jeremy Rodriguez
> All Solar
> CO. USA
> 
> 
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 



More information about the RE-wrenches mailing list