[RE-wrenches] Enphase / Inverter failures

matt at solar-energy-solutions.com matt at solar-energy-solutions.com
Fri May 10 05:01:34 PDT 2013


Corey,

Thanks for sharing this helpful information.  I decided to test M190s on
my shop in early 2010 before offering a new product.  Until about 8 months
ago, when we started seeing engineers specify Enphase, I refused to
install more of the units.  My breakdown in Midwest climes:

- M190 - 9/15 = 60% failure
- M215 - 1/146 = 1% failure


Matt


Matthew Partymiller
Solar Energy Solutions LLC
(859) 312-7456
matt at solar-energy-solutions.com


> I would be interested in hearing about other wrenches' observed Enphase
> failure rates.
>
> Since 2010 we've installed 1347 total Enphase units with an overall
> failure
> rate of 3.27%
>
> Our breakdown is as follows:
>
>    - M190 - 19/362 = 5.25% failed
>    - M210 - 21/545 = 3.85% failed
>    - D380 - 3/101 = 2.97% failed
>    - M215 - 1/339 = 0.29% failed
>
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA