Thanks everyone, John, from your SMA days, can you predict if the 6000US
will get stuck on a local MPP?

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John Berdner
Sent: Monday, April 29, 2013 3:12 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] unbalanced string voltages

 

Kirk:

 

As noted below the current will be shared by all modules in the string and
the voltage will be the sum of the operating voltage at that current.

When mixed modules are used this results in differences between the
operating voltages of each string in the system.

Having parallel strings with differing max power points will have an effect
on the operation of the MPP tracker.

You should also consider the effect of the mixed modules on the MPPT of the
inverter (or charge controller) and resultant reductions in energy yield.

 

Some inverters can "get stuck" on one of the a local MPP voltage as opposed
to global MPP

This will reduce the overall energy yield - sometimes significantly.

A good max power point tracker will find the correct global MPP voltage.

The global MPP will be at a point that is between the upper and lower
operating voltages of all the parallel strings and proportional to the
current of each string.

Using your example Strings 1, 2 and 4 are close in voltage.

For simplicity I will consider them to be the same, i.e. approximately 389
Vdc with 2 strings at 3.6 Amps and 1 string at 5.5 Amps = 12.7 Amps

String 3 will be about 378 volts and 3.6 Amps.(the lower of the two module
currents)

Note: You can calculate this voltage of string 3 more closely by looking at
the IV curve of the higher current module when running at the lower current,
i.e. this module will operate closer to Voc so the MPP voltage of this
string will be slightly higher.

 

Using the numbers from your email, the voltage difference is 11 Vdc and the
ratio of the currents is 0.779 = 12.7/(12.7+3.6) so the global MPP voltage
should be about 8.6 volts (= 11*0.779) above that of string 3.

I would therefore expect global maxima to be around 386-387 Vdc (378 + 8.6
V) above the voltage of string 3.

Using 387 Vdc as an operating point you can estimate the mismatch power loss
from the IV curves of the various modules.

String 3 will be operating above it's MPPT so the modules will be closer to
Voc and the current will be reduced further and the overall power of that
string will be lower.

Since the current changes as the modules move towards Voc you will need to
iterate the calculation a couple of times to get close to the actual
operating point and estimated reductions in energy yield.

 

Best Regards,

 

John Berdner

General Manager, North America

 

SolarEdge Technologies, Inc.

3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new
address.)
T: 510.498.3200, X 747

M: 530.277.4894 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Monday, April 29, 2013 10:41 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] unbalanced string voltages

 

Modules aren't exactly constant current devices. I-V curve
They are for much of their voltage range, up to a voltage a bit below the
MPP, and then the current starts tapering down to 0 at Voc.  The entire
string can only pass as much current as the lowest current module.  That
means the higher current module will be forced to operate where it can,
which is at a higher voltage than its MPP point, as David said.  
If you don't believe us, hook up a couple of mismatched modules and measure
voltage across each module, and the current. Current is always equal in a
series connection, then the modules make up for it by moving up or down
along their IV curve.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/29/2013 9:44 AM, Larry Crutcher, Starlight Solar Power Systems wrote:

David,  

 

Since a PV module is a constant current device, I don't believe this will
take place. For a given amount of light (plus all factors affecting power),
the current potential will be there. What force can act upon the current to
reduce it? Consequently, the lowest Vmp the inverter can track will dictate
the voltage for all strings. This means less power from the highest Vmp
modules. Do you agree? 


Larry Crutcher






 

On Apr 28, 2013, at 9:33 AM, David Katz <dkatz at aeesolar.com> wrote:

 

Kirk

The 43volt 5.5 amp panel will operate at 3.6 amps, so it's voltage will move
up toward open circuit voltage, raising the mppt voltage of that string.  I
would bet that the voltage of that entire string will rise to match the
higher voltage string by moving toward open circuit voltage.  It should work
fine.

David Katz

Sent from my iPhone


On Apr 28, 2013, at 9:01 AM, "Kirk Herander" <kirk at vtsolar.com> wrote:

Hello everyone,

 

I am at present adding to a -20- panel array of old Sanyo HIT "lipped" 200
watt panels. They are configured in -4- series strings of -5- panels, with a
string MPP voltage of 279 vdc (55.8 v, 3.6 a each). The customer wants to
add another nominal 2 kw using the (now) Panasonic 235 watt HIT's which have
an MPP of 43.0 vdc, 5.5 a. I am locked in to an existing SMA 6000US
inverter. Obviously I cannot get all the strings to the same voltage. But I
can get relatively close by rewiring:

 

String 1: -7- 200 watt @ 55.8 ea. = 390.6 v MPP

String 2: same as string 1

String 3: -6- 200 watt @ 55.8 plus -1- 235 watt @ 43.0 = 377.8 v MPP

String 4: -9- 235 watt @ 43.0 = 387 v MPP

 

Under this scenario there is a delta of about 12 vdc between high and low
MPP. I assume the entire array will operate at the 377.8 V MPP. I know that
the 235 watt panel will be current limited also in string 3. Am I missing
anything obvious in doing it like this? How will the inverter arrive at an
operational MPP voltage?

 

PS. In a pinch I could install a leftover 200 watt HIT I have in the shop.
That way I could have -3- strings of -7- 200's @ 390.6 v MPP, and one string
of 235's @ 387v MPP. But I would prefer not to use this panel since the
frame is damaged.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 





_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
for the use of the individual or entity who is the intended recipient and
may contain information that is privileged, confidential and exempt from
disclosure or any type of use under applicable law. If the reader of this
e-mail is not the intended recipient, or the employee, agent, or
representative responsible for delivering the e-mail to the intended
recipient, you are hereby notified that any dissemination, distribution,
copying, or other use of this e-mail is strictly prohibited. If you have
received this e-mail in error, please reply immediately to the sender. 

P  Please think of the environment before printing this email

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130430/8d0f4a01/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 11868 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130430/8d0f4a01/attachment-0007.gif>


More information about the RE-wrenches mailing list