Bill,

 

Does this mean that USE-2 is not acceptable for use in this manner?

Also, what is your confidence level that this will make it to the printer? I
recall a few other instances of proposed amendments that at the last minute
were not included in the past few code cycles (pertaining to PV).

 

Too bad we are still on the 2008 code cycle here.

 

Thanks

Glenn Burt

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Monday, March 25, 2013 10:54 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Cable tray

 

All,

 

Here is the language that has been accepted into the 2014 NEC:

 

690.31(C)(2)

 

(2) Cable Trays. PV source circuits and PV output circuits using
single-conductor cable listed and labeled as Photovoltaic (PV) wire of all
sizes with or without a Cable Tray marking/rating shall be permitted in
cable trays installed in outdoor locations provided the cables are supported
at intervals not to exceed 30cm (12 in.) and secured at intervals not to
exceed 1.4m (4.5').

 

I hope this helps. It is a very big deal.

 

Bill.

 

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Monday, March 25, 2013 6:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cable tray

 

Ouch. I promise I'm not advocating for anything like that. What I may be
missing is the Code reference that says "no cable tray on roofs" or similar.


 

There is so much room for improvement in wire management practices, that
being able to use cable tray seems like a step forward. I understand some
jurisdictions do not allow it, but it appears as though Code changes were
made specifically to address this. It's boring stuff, but you can read the
explanation of the Code changes in the ROP and ROC documents. 

 

The Code changes a lot with regards to PV system, and Article 690 is more
fluid than other articles. Some of this is the Code trying to keep up with
technology. In other cases the Code evolves based on new applications for
existing products. Often it changes because some areas of the Code are
confusing for electricians and inspectors alike. If the new Code language is
more clear in its intent than previous versions, some inspectors are willing
to let installers build to the most current standard.

 

That's all I'm advocating for: Trying to understand how the minimum
requirements outlined in Code evolve over time so that you can have a
friendly and informed conversation with your AHJ over a donut. 

 

 

 

 

On Mar 25, 2013, at 6:26 PM, William Miller wrote:

 

David:

This is great news.  Now, whenever I want to do something that is prohibited
by code, I can just say that the Code Making Panel is gonna correct that
pesky code section (insert your problem citation here) any day now, so I
might as well be allowed to do whatever it was I was fixin' to do anyway.
Unless I am missing something...

Thanks!

William Miller

PS:  Just kidding.  Hope no offense is taken.

wm


At 03:46 PM 3/25/2013, you wrote:



So if you ever get called on 392.10(B)(2), I think you can point out that
the Code Making Panels have been busy clarifying that cable tray is okay for
source circuit conductors. Unless I'm missing something....

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130326/8fbb7e47/attachment-0004.html>


More information about the RE-wrenches mailing list