[RE-wrenches] Sick pack
Tump
tump at swnl.net
Thu Dec 19 05:52:00 PST 2013
What is the Spg (use a good refractometer)of each cell 1.11?1.15? that temp is not to hi especially w/ the temp comp. Charging w/ the unit in bulk, the inverter will see voltage rise quickly and decide that they are charged. disconnect the batteries and check as individual units Eq at high voltage `32 v and a low charge rate 10 amps, watch the temp Spg . I would suggest that if at all possible remove 2 sets and eq from the grid for ~week on /off.DO use a temp sensor and watch the spg. See Surrette's tech bulletin re/ highly sulfated batteries. www.surrette.com.
Anything over 2 strings will cause a headache, BUT thats more the norm w/ the cheep off grid, I'm going to manage my gen run time kinda of folks!
On Dec 19, 2013, at 1:28 AM, frenergy wrote:
> Gentlemen and women,
>
> I have been called in to deal with a pack of 16 (4 strings of 4 for 24V), L-16s, 6 years old. She is having to run her generator 2 times a day. Here in N.E. CA. its been cold, mostly clear, little wind. Her inputs are about 1 KW of PV, and small wind machine and of course a serious generator. Cables and terminals looked clean, were tight. The bulk setting on the Trace 4024 was 28.0 V for 2 hrs with RTS, however, she would manually turn off the generator soon after it reached 28V. Recipe for suphation.
>
> Rather than getting into too much detail, here's my quandary. When I fired up the generator, the input amps in each of the 4 strings were.... string #1:29A, 2:34 A, 3:25 A, 4: 13 A. A survey of IR temps throughout the pack gave temps ranging from 63 to 92 degrees. The highest temps were in the string pulling highest amps. In trying to find shorted/failed and/or sulphated cells which data are most relevant? Temps, amp draw during charge, disconnect strings from each other and check volts of each 6 volt batt?, active bubbling? ...all the above?
>
> I'm thinking I should have (1) checked the amp draw with batts under load/genny off in each string AND (2) check amps between strings with the pack at rest, no input or output. I would love to EQ the pack but with a temp already in the 90's and uneven currents in the strings I don't want to risk too high of temp or worse, a runaway situation and fire. I'm thinking I'd like to yank a few bad batts and run on 3 strings and then carefully EQ.
>
> I appreciate any insights.
>
> Thanks in advance,
>
> Bill
> <FRS_working_logo.jpg>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> Tump at swnl.net www.SWNL.net
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>
> ******** MAINE'S CHARTER ********
> Trace Xantrex "Certified" Dealer / Installer"
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131219/6fa81744/attachment-0003.html>
More information about the RE-wrenches
mailing list