[RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Eric.Bentsen at schneider-electric.com
Eric.Bentsen at schneider-electric.com
Mon Nov 11 11:49:51 PST 2013
Hi Wrenches,
There is no "implication" other than confirming how the disco
is tested, and thus certified. It probably makes no difference
electrically which position the
unit is mounted, but AHJs may have differing opinions on whether this
would be permitted.
Rgds,
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Bob-O Schultze <bob-o at electronconnection.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
11/11/2013 10:09 AM
Subject:
Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Dan,
I think this thread applied not to OCDs but to an unfused 600VDC
disconnect can mounted on a roof which is less than vertical.
Bob-O
On Nov 11, 2013, at 9:21 AM, Exeltech wrote:
Wrenches,
There appears to be some misinformation getting into this thread.
The "trip" mechanism within standard thermal over-current protective
devices ("OCP devices") is mechanically spring-loaded, and is triggered by
heat.
Eric mentions below that Square D breakers are tested in a vertical
orientation only - the implication being that's their only "UL certified"
position. If this were true, it would imply the breakers cannot be used
in any other orientation. This would potentially limit the Square D OCP
market to sub-panels and other enclosures where the devices are vertical.
Inasmuch as the vast majority of panelboards I've encountered in my 40+
years in this industry have the breakers stacked horizontally, it would
not be a wise business decision for the manufacturer to self-inflict such
a limitation on their product.
This also does not mean any such limitation (real or not) applies to all
breakers.
By way of example, OCP devices work in a horizontal position, stacked
"pancake" style in a main panelboard, as well as vertically oriented
side-by-side in a sub-panel. In either orientation, they are in full
compliance with UL 489, (UL Standard for Circuit Breakers, Switches, and
Circuit Breaker Enclosures). If an OCP device *was*
positionally-sensitive, UL Standards require this sensitivity to be noted
in the documentation accompanying the device. Further to that point, UL
489 Section 7.1.1.13 states: "In determining if a circuit breaker complies
with the test requirements, the device shall be mounted or supported as in
service and tested under conditions approximating those of intended
operation, except as otherwise noted."
Mounting position notwithstanding, a greater concern would be the ambient
temperature of a rooftop location, whereby summer heat would tend to make
the OCP device more sensitive than necessary, potentially causing it to
trip at an amperage below that of its UL ratings. While a nuisance, a
more serious issue arises when operating the OCP device in cold ambient
conditions, whereby the device may allow MORE than its rated trip current
to flow.
Per UL 489, OCP devices are tested at either 25C or 40C ambient. Again
per UL 489, if an OCP device is to be used in ambient conditions other
than those two ranges, the acceptable temperature range for that OCP
device shall be marked on the body of the device.
In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3, mechanical
vibration testing is conducted with OCP devices oriented vertically,
horizontally, and inclined 30 degrees from vertical, with all devices
energized up to 200% of the device rated current during the testing.
Given the preceding, and per implication of UL 489 testing methods, OCP
devices are NOT positionally sensitive.
In conclusion, if you DO install a rooftop OCP system, and for proper
protection, please ensure the OCP devices utilized are rated for the
worst-case ambient temperatures involved.
Regards to all,
Dan Lepinski
At 09:33 AM 11/8/2013, you wrote:
Hi Kirpal,
All Square D safety switches are UL tested in the Vertical position ONLY,
so if someone is trying to install a switch in any other position other
than vertical, that will be between them and the inspector.
Hope this helps.
Eric
____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES
| Technical Support Representative
Phone: +(650) 351-8237 ext. 001# | Email:
eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131111/08154e16/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131111/08154e16/attachment-0003.jpe>
More information about the RE-wrenches
mailing list