Fri Oct 18 09:26:44 PDT 2013
Marco,
Besides the good responses you have already received, 20-30kW, 480V machines are really targeting larger installations that would be on facilities with 480V. I would generally not build a system with 480V inverters on a 208V service. For large systems, there are large inverters running at 208V, for small systems there are plenty of single-phase units that would work just fine. Incidentally, read the new NEC 705.100 in the 2014 code. It clarifies that utilities should not be disallowing single-phase units on a 3-phase service. The typical utility concerns do not understand how the equipment works.
(A) Single Phase. Single-phase inverters for hybrid systems
and ac modules in interactive hybrid systems shall be
connected to three-phase power systems in order to limit
unbalanced voltages to not more than 3 percent.
Informational Note: For utility-interactive single-phase inverters,
unbalanced voltages can be minimized by the same
methods that are used for single-phase loads on a three- phase
power system. See ANSI/C84.1-2011, Electric Power Systems
and Equipment — Voltage Ratings (60 Hertz).
This is a huge change from the way it was previously written. You can thank me next time I see you with a beer. This was my proposal.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf
Sent: Thursday, October 17, 2013 9:31 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] smaller 3-phase commercial inverters
Yeah, lots more choices out there in the 10+ to 30 kW range….but pretty much all of the larger capacity models only come at 480V.
Anyone know why? We have way more 120/208V applications here in Hawaii than 277/480.
marco
Chris Mason wrote:
>SMA just came out with their Sunny Tripower line for the US.
Yes those are interesting. But they are only for 480 Wye, not 240 Delta.....
Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240 3-phase with a hi-leg (stinger)?