[RE-wrenches] 3-Phase Service, One Phase Fails

Chris Mason cometenergysystems at gmail.com
Tue Sep 24 09:56:20 PDT 2013


Real simple. A contactor with a phase loss detector gadget.

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer™
Renewable Energy Systems professional
Generac Generators Factory technician
On Sep 24, 2013 11:12 AM, "Karl Jaeger" <kjaeger at lightwavesolar.com> wrote:

>  Greetings Esteemed Wrenches,****
>
> We are building a 35.75kW project with (6) Power One 6000’s. The service
> is a 240 delta. The utility is requiring (late in the game) that if one leg
> of the service is lost, all inverters must shut down. Of course, we have
> two inverters that do not shut down in that circumstance because they are
> only tied into the other two phases. SMA has a good (cheap) option to deal
> with this, SMA Power Balancers. With other inverters this can be
> accomplished by installing an ATS with an integrated controller by
> programming in the unacceptable phase imbalance (expensive). Does anyone
> have experience with this requirement and/or have a good (cheaper) solution?
> ****
>
> Thank you in advance!****
>
> ** **
>
> Karl Jaeger****
>
> LightWave Solar ****
>
> Nashville, TN****
>
> ** **
>
> ** **
>
> ** **
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130924/56c5b13f/attachment-0003.html>


More information about the RE-wrenches mailing list