[RE-wrenches] 200 Amp Main Equip for 60A Solar
Dave Click
daveclick at fsec.ucf.edu
Thu Jun 13 05:32:32 PDT 2013
Jeff,
This has been sent out on the list a few times but I don't remember
anyone sharing their personal experiences with it:
http://solarprofessional.com/articles/products-equipment/product-launches/milbank-offers-load-tap-connector
200+ 60 for a meter main is trickier. The $1100 (list) Schneider
RC2M200S lets you do a 200A main and a 50A PV breaker (interconnecting
on line side of the 200A), which may be close enough for you depending
on your system details (10kWac @ 240V -> >52.1A breaker).
DKC
On 2013/6/12 21:09, Jeff Clearwater wrote:
> Hey Wrenchies,
>
> Anybody know of a 200 Meter base with lugs rated for dual wire so we can
> do a 60 Amp Supply side solar feed on a 200 Amp service?
>
> Or does anyone know the right equip to get to ensure we can install 2
> dual lug taps on both single lugs? (a meter base with enough room for
> the T lugs?)
>
> Or better yet any integrated 200 Amp Service / Meter equipment that has
> an accessible spot to tap 60 Amps for a Disconnect on the meter side of
> the Main?
>
> I have 2 SB 2500Us existing and want to add a single SB 5000TLUS - I
> show rated output to be 46 Amps total and hence a 60 Amp needed.
>
> Advice my esteemed colleagues?
>
> Thanks,
>
> Jeff
>
> --
> Jeff Clearwater
> Village Power Design
> Renewable Energy Design & Installation
> Ecovillage Design Consultant
> www.villagepower.com
> 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list