[RE-wrenches] Old Modules for GIT system?
Brian Teitelbaum
bteitelbaum at aeesolar.com
Tue Jun 4 16:00:21 PDT 2013
There's copper in them thar hills!
You might even be able to buy 1kW of new PV with that.
But is your math wrong? 24 x 80W = 1920W not 960W.
Have you tested these modules? Solarex does not have a great track record. The APT PowerCenter puts this back about 20 years, so they aren't exactly young modules.
Brian Teitelbaum
AEE Solar
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Tuesday, June 04, 2013 3:11 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Old Modules for GIT system?
I forgot to add to add we have 220' of 4 X 4/0 Thhn running to the house. With today's prices I could pull that out and purchase a couple of the Enphase inverters
____________________________________________________________________________
Dana Orzel
Great Solar Works, Inc - NABCEP # 051112-136
dana at solarwork.com<mailto:dana at solarwork.com> - www.solarwork.com<http://www.solarwork.com>
O - 970.626.5253 F - 970.626.4140 C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"
From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steven Lawrence
Sent: Tuesday, June 04, 2013 3:53 PM
To: re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Old Modules for GIT system?
Dana,
Maybe wire 3 in series to a single Enphase? It'll depend on what the voltages are.
Date: Tue, 4 Jun 2013 14:01:42 -0600
From: "Dana" <dana at solarwork.com<mailto:dana at solarwork.com>>
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: [RE-wrenches] Old Modules for GIT system?
Message-ID: <05f401ce615e$55773960$0065ac20$@com>
Content-Type: text/plain; charset="us-ascii"
I have a client eat has a 24 - Solarex SX 80 PV module system that was off
grid, Trace inverter, APT Power panel and an very aged L-16 battery bank.
The utility came in and he wants to go grid tie. It is or was only 960 watt
originally. I realize that an array rewire is in order and it may only be a
1 KW system but he is interested in getting the equipment upgraded.
Has anyone done a grid tie with such a small array and with modules this
old?
Any thoughts on installing sealed batteries and leaving it alone?