[RE-wrenches] Combining conductors
Nathan Stumpff
Nathan at arcticsun-llc.com
Thu Apr 4 10:20:05 PDT 2013
Larry,
I don't think the relationship of AWG size to ampacity is a linear curve, so while that "rule of thumb" may be pretty good, you can't always count on it. I would use the circular area column in NEC Chapter 9, Table 8 for an easy, quick way to compare two of one conductor vs. one of another.
Of course there are other code issues regarding parallel conductors...
Cheers,
-Nathan
--
Nathan J. Stumpff
NABCEP Certified PV Installer #091209-175
NABCEP Certified Solar Heating Installer #032412-14
Project Manager | Arctic Sun, LLC
nathan at arcticsun-llc.com <mailto:nathan at arcticsun-llc.com> | (907) 457-1297
www.reina-llc.com<http://www.reina-llc.com> | www.arcticsun-llc.com<http://www.arcticsun-llc.com/>
[cid:image001.png at 01CE3115.44031510]<http://www.facebook.com/ArcticSunLLC>
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems
Sent: Thursday, April 04, 2013 8:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Combining conductors
Wrenches,
Here's a tough one for me to understand. I am installing 2 volt AGM batteries. There are two terminals for each battery polarity. I have some height limits so I need to use the minimum wire size. Here's my question: If I combine two identical conductors, what is the equivalent single conductor size?
I found one "rule of thumb" that says doubling like conductors creates a AWG decrease of 3. Example: two #2 will be equivalent to 2/0. Is this true?
Thank you,
Larry Crutcher
Starlight Solar Power Systems
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130404/dcedc6dc/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 2272 bytes
Desc: image001.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130404/dcedc6dc/attachment-0006.png>
More information about the RE-wrenches
mailing list