I'm with your inspector on this.

I don't install fuses or breakers on roofs

jay

peltz power


On Feb 7, 2013, at 12:02 PM, Jason Szumlanski wrote:

> While I haven't completely convinced the latest inspector about PV not being mechanical equipment, I'm running into another issue. 
> 
> I decided to try out the new Midnite MNPV6-AC combiner for Enphase circuits. Because there are overcurrent devices inside, the inspector now insists that NEC 240.24(A) applies and that the enclosure must be readily accessible, meaning you have to reach it without a ladder. That would seem to make the MNPV6-AC as a roof mounted solution, or Soladeck combiner boxes, or any other combiner box incorporating overcurrent protection, pretty much useless on a pitched roof or flat roof without a permanent access ladder or hatch. 
> 
> I'm debating whether to go to battle on this one or just capitulate. 
> 
> Jason Szumlanski 
> Fafco Solar
> 
> P.S. To answer benn's question, there is no definition of 'mechanical,' but it does define 'equipment,' and it's clear to me that PV does not fit the description.