[RE-wrenches] high insolation value and inverter undersizing

Chris Mason cometenergysystems at gmail.com
Mon Jan 28 16:15:47 PST 2013


The initial issue was concerned with waste power, but that presumes all
power is priced evenly. Take a familiar situation, you specify and sell the
system based on a number of 240W modules. Let's presume time passes and
when you go to buy out the job, you find there is a deal on 260W modules
which makes them as cheap as the 240W would have been. Why would you not
just buy the larger output if all costs are the same. If they clip the
inverter a little, oh well.



On Mon, Jan 28, 2013 at 7:35 PM, Nick Soleil <nsoleil at enphaseenergy.com>wrote:

> Hi John,
>
> It's important to clarify that the "clipped" power does not turn into heat
> within the microinverter. The microinverter only draws enough current to
> achieve it's max output rating, and the remaining current is "left in the
> module", so to speak. So, the heat generated at peak times is the same,
> whether using a 260W module or a 280W module.
>
> Many string inverters actually work similarly. What's different for them,
> however, is their overall thermal situation. The primary thermal driver for
> a string inverter is the amount of heat generated by their electronics, and
> the ability of their "fans & fins" to expel that heat.
>
> For example, a 5kW string inverter generates ~200W of heat at peak, and it
> has fans and fins sized accordingly.  But, the effectiveness of the fans
> and fins depends on the ambient temperature (and on elevation/air mass),
> and if your inverter was operating at max power during hot weather (which
> would require significant oversizing due to the modules' temperature
> derates), it could exceed the capability of the fans and fins. This would
> then require the inverter to ramp-down output.  (Actually, some string
> inverters can respond improperly--depending on whether their fan is
> continuous, load-controlled or thermally-controlled--and actually fry the
> electronics.)
>
> But, the thermal environment of a microinverter is very different.
>
> The main thermal driver in our situation is actually the external
> environment, not the electronics. Regardless of sizing ratio, an M215
> generates less than 10 watts of heat at peak, whereas the heat radiated
> from the module at peak times will be substantially greater than that.
> Consequently, we've already over-engineered the microinverter for extreme
> heat management, and the thermal effects of sizing ratio are simply a drop
> in the bucket compared to the other factors.
>
> For that reason, we don't put limits in our warranty with regard to sizing
> ratio (which contrasts with at least some string inverter warranties), and
> we would not expect to see any microinverter ramp-down behaviors driven by
> sizing ratio.
>
>
>
>
> On Mon, Jan 28, 2013 at 11:06 AM, John Berdner <John.Berdner at solaredge.com
> > wrote:
>
>>  Jason:****
>>
>> ** **
>>
>> Be careful of drawing false comparisons.  There is no free lunch.****
>>
>> Beyond the energy yield issues there are some reliability issues.****
>>
>> ** **
>>
>> You should also consider that running an inverter flat out all the time
>> will shorten it’s life (due to the Arrhenius effect).
>> http://en.wikipedia.org/wiki/Arrhenius_equation****
>>
>> ** **
>>
>> Think of the inverter temperature in the same way you would the power
>> output curve (the two are closely related).  Moving the whole power curve
>> up “more on the shoulders” also moves the whole temperature curve up as
>> well.****
>>
>> The average lifetime (all this stuff is only probabilities) was projected
>> with certain assumptions about how many hours at what temperature.  As
>> module sizes increase a given inverter will spend more time at a higher
>> power level, i.e. runs hotter longer, which non-linearly reduces the life
>> of the product.****
>>
>> ** **
>>
>> Just my $0.02… With the high labor cost of replacement it might be better
>> to undersize the module relative to the power electronics or vice versa.
>>  This may or may not increase the installed system cost depending on the
>> products you choose. Running everything flat out all the time is probably
>> not the greatest idea.  ****
>>
>> ** **
>>
>> Best Regards,****
>>
>> ** **
>>
>> John Berdner****
>>
>> General Manager, North America****
>>
>> ** **
>>
>> [image: SmallBannerPictEngnew]****
>>
>> ** **
>>
>> SolarEdge Technologies, Inc.****
>>
>> 3347 Gateway Boulevard, Fremont CA 94538 USA  *(*Please note of our new
>> address.)*
>> T: 510.498.3200, X 747****
>>
>> M: 530.277.4894 ****
>>
>> ** **
>>
>> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
>> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason
>> Szumlanski
>> *Sent:* Monday, January 28, 2013 5:30 AM
>>
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] high insolation value and inverter
>> undersizing****
>>
>> ** **
>>
>> I found the latest module "rightsizing" paper by Enphase pretty
>> interesting. It does stand to reason that there are a lot of hours in the
>> day where the inverter is producing less than rated power, so increasing
>> the module size makes sense. Obviously there is an optimum point in every
>> system where clipping exceeds gains, but that's virtually impossible to
>> nail down due to so many factors being involved. I think the point would be
>> that PV mods are coming down in price so much that "rightsizing" is
>> basically equivalent to "upsizing," within reason, of course. Spending an
>> extra 25% on PV might increase the installed system cost by 5-10%.****
>>
>> *Jason Szumlanski*****
>>
>> *Fafco Solar*****
>>
>> ** **
>>
>> On Sun, Jan 27, 2013 at 6:00 PM, Marco Mangelsdorf <marco at pvthawaii.com>
>> wrote:****
>>
>> I have had a concern for a long time that as PV modules have gone up in
>> output that there is inevitably going to be more and more clipping taking
>> place as they’re paired with comparatively lower output inverters.  In
>> effect, matching, say. a 260-watt module with a micro inverter with a max
>> output of 225 watts reduces that 260-watt mod to 225 watts.  It’s not a
>> matter of if clipping will take place, but how much and how much actual
>> harvestable energy will be lost.****
>>
>>  ****
>>
>> Out here in the tropics, even in January with the lower sun angle, we see
>> irradiance levels well above 1,000 watts/square meter range.  Take a look
>> at what I copied today from a weather station that we installed at nearby
>> installation.****
>>
>>  ****
>>
>> Given the clipping issue inherent in using undersized inverters, it seems
>> to me that moving to larger output micros makes a whole lotta sense.  I’ve
>> got one of the first installs using the Power-One 250-watt and 300-watt
>> micros and am so far quite impressed.  Why use a 225-watt rated micro with
>> a 225-watt or higher output mod when larger micros are now readily
>> available?****
>>
>>  ****
>>
>> What are the views out there regarding this clipping issue?  Is it as
>> minimal as our Enphase friends suggest in their latest white paper or more
>> of an issue as I conclude?****
>>
>>  ****
>>
>> marco****
>>
>>  ****
>>
>>  ****
>>
>> Environmentals from Weather Station at a Hilo, Hawaii installation****
>>
>> * *****
>>
>> Sunday, January 27th 2013, 12:40:00 pm****
>>
>> ****
>>
>>  ****
>>
>> *Ambient Temp.* 25.30 °C****
>>
>> *Cell Temp.* 41.70 °C****
>>
>>  ****
>>
>> ****
>>
>>  ****
>>
>> *Insolation* 127.81 kWh/m²****
>>
>> *Irradiance 1,175.00 W/m²*****
>>
>>  ****
>>
>> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
>> for the use of the individual or entity who is the intended recipient and
>> may contain information that is privileged, confidential and exempt from
>> disclosure or any type of use under applicable law. If the reader of this
>> e-mail is not the intended recipient, or the employee, agent, or
>> representative responsible for delivering the e-mail to the intended
>> recipient, you are hereby notified that any dissemination, distribution,
>> copying, or other use of this e-mail is strictly prohibited. If you have
>> received this e-mail in error, please reply immediately to the sender.
>>
>> *P*  Please think of the environment before printing this email
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
>
> Cordially,
>
> *Nick Soleil*
>
> *Field Applications Engineer
> *
>
> *Enphase Energy*
>
> Mobile: (707) 321-2937
>
>
> **
>
> *Enphase Commercial Solar.* *Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
>
> *
> *<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
>
> 1420 North McDowell
>
> Petaluma, CA 94954
>
> www.enphase.com <http://www.enphaseenergy.com/>
>
> P: (707) 763-4784 x7267
>
> F: (707) 763-0784
>
> E: nsoleil at enphaseenergy.com
>
> [image: nabcep logo] Certified Solar PV Installer #03262011-300
>
> “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
> to fission. And it just so happens that there’s an enormous fusion reactor
> safely banked a few million miles from us. It delivers more than we could
> ever use in just about 8 minutes. And it’s wireless! .”
>
> - William McDonough
>
>
> This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message.
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts