Hi Allen,
Now that you have me thinking.....if you look at the charge recommendation 
for T-105 and L16, according to Trojan,
 they are giving us a range of 2.35-2.45V per cell @77degF.
If there is no variable other than temperature, why the range?
http://www.trojanbatteryre.com/PDF/datasheets/L16REA_TrojanRE_Data_Sheets.pdf
http://www.trojanbatteryre.com/PDF/datasheets/T105_TrojanRE_Data_Sheets.pdf

Rgds,
_____________________________________________________________________________________ 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bentsen at schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 

----- Forwarded by Eric Bentsen/Canada/Schneider on 08/07/2013 01:53 PM 
-----

From:
Eric Bentsen/Canada/Schneider
To:
Allan at positiveenergysolar.com, RE-wrenches 
<re-wrenches at lists.re-wrenches.org>
Date:
08/07/2013 01:41 PM
Subject:
Re: [RE-wrenches] Trojan L-16s


Hi Allen,
I am going by experience, not only with my own (4) Workaholic L16s, but 
when dealing with customers in the field.
 I would like to get some feedback from other wrenches on this.
 Maybe it is coincidence, but there seems to be a correlation. Maybe the 
taller batteries 
experience sulfation easier?
 
Rgds,
_____________________________________________________________________________________ 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bentsen at schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar <allan at positiveenergysolar.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
08/07/2013 12:59 PM
Subject:
Re: [RE-wrenches] Trojan L-16s
Sent by:
re-wrenches-bounces at lists.re-wrenches.org



Eric,
I kept this in my inbox for awhile, and finally had to ask - where did you 
get this information? I have never heard this recommendation - to charge a 
taller flooded lead acid battery to a higher voltage just because it's 
taller. I guess I see the apparent logic - more gassing addresses a 
potential for more stratification of the electrolyte - but if true, why 
have I never seen this in any battery service guide? What's your source? 
And has anyone else heard of this?
Thanks, Allan

Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 7/16/2013 7:53 AM, Eric.Bentsen at schneider-electric.com wrote:

Hi Drake, 
The L16 is quite popular in RE apps...but they typically require a bit 
higher charge voltage to reach the correct SOC than their shorter 
counterparts (i.e. T105 golf cart), 
because they are a taller battery (stands to reason .....specific 
"gravity"). Make sure they are in a vented enclosure if off-gassing will 
be an issue. 
Eric
_____________________________________________________________________________________ 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bentsen at schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/e6b08f6c/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/e6b08f6c/attachment-0004.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/e6b08f6c/attachment-0005.jpe>


More information about the RE-wrenches mailing list