[RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service
Pekka Laine
pekka at photonsolarpower.com
Mon Jun 17 10:33:49 PDT 2013
Dear Fellow Wrenches,
We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A. We are landing those into a dedicated load center with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 160A breaker. This also equals to the maximum we can backfeed into a 800A/800A Main Service on the load side according to the "120%" rule.
The problem now is that we cannot locate any kind of 160A breaker or even a 160A fuse for a AC disconnect.
Has anybody ever done this without doing a "line-side tap?" It is hard to believe that there wouldn't be an existing solution to landing maximum PV into a 800A service. Are we missing something?
Any good ideas or comments would be appreciated.