[RE-wrenches] EGC vs GEC, separately derived system

Jason Szumlanski jason at fafcosolar.com
Thu Nov 29 07:12:22 PST 2012


We typically run a #6 combined EGC/GEC on all residential systems just to
keep it simple. The cost difference is typically negligible. We use
irreversible C-crimps to combine the wires in a roof mounted junction box.

*Jason Szumlanski*

*Fafco Solar*


On Wed, Nov 28, 2012 at 10:56 PM, mac Lewis <maclewis1 at gmail.com> wrote:

> Hello wrenches,
>
> What constitutes a separately derived system?  Would you consider a
> breaker tied enphase system a separately-derived system?  Suddenly,
> inspectors in our AHJ are considering all PV systems separately derived
> systems and thus requiring applying GEC sizing (as opposed to EGC sizing)
> from the inverter(s) to the tie in point.  This does not jive with my
> understanding.  Would like to hear other thoughts about this.
>
> Here is the definition of a separately derived system as per 2008 NEC
> Article 100 Definitions:
>
> *Separately Derived System*:  *A premises wiring system whose power is
> derived from a source of electric energy or equipment other than a service.
>  Such systems have no direct electrical connection, including a solidly
> connected grounded circuit conductor, to supply conductors originating in
> another system.*
>
> For your enphase systems do you size your ground from roof to the breaker
> panel as an EGC or a GEC?
>
>
> Thanks in advance for your thoughts.
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
> *
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121129/0001846e/attachment-0004.html>


More information about the RE-wrenches mailing list