[RE-wrenches] Hydro Diversion Controls

jay peltz jay at asis.com
Thu Nov 22 11:22:55 PST 2012


Hi William

If the hydro is only 2 amps, I would argue that you don't diversion at all.

The float current expect for a really small battery bank is higher than that.

So unless you want/need it for some other reason, I would not install one.

jay

peltz power
On Nov 22, 2012, at 11:18 AM, William Miller wrote:

> David:
> 
> Interesting idea.  The added benefit is if the relay gets stuck, it won't destroy the battery bank.
> 
> The diversion load must equal or exceed the output of the hydro, correct?  The load we have will draw 38 amps at 24 vdc, the hydro will put out 2 amps.  Sounds like I have enough headroom
> 
> Thanks again to all of you.
> 
> William
> 
> At 08:32 PM 11/21/2012, David Katz wrote:
> 
>> William,
>> I always connect the hydro side of the diode to the diversion load with the contactor, so I don't pull the battery down while regulating.  The diversion load must draw enough current to pull the hydro voltage below the absorb voltage. Use ohms law to calculate the resistance.
>> David Katz
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 




More information about the RE-wrenches mailing list