Seems if the Romex is not listed as being suitable for use in a wet
location, having not been tested by UL for that situation, it would not be
suitable for use in that environment, regardless of how its internal
conductors are rated.

 

Glenn Burt

 

From: Ray Walters [mailto:ray at solarray.com] 
Sent: Friday, October 26, 2012 10:28 PM
To: glenn.burt at glbcc.com; RE-wrenches
Subject: Re: [RE-wrenches] Enphase and Romex

 

So if the Romex is loaded with THHN/THWN (damp/wet rated), and no where does
the outer covering of the Romex itself get exposed to the wet location, that
should be sufficient? 

Ray Walters

On 10/26/2012 7:45 PM, Glenn Burt wrote:

300.9 Raceways in Wet Locations Above Grade.

Where raceways are installed in wet locations abovegrade, the interior of
these raceways shall be considered to be a wet location. Insulated
conductors and cables installed in raceways in wet locations abovegrade
shall comply with 310.8(C).

 

"Section 300.9, new for the 2008 Code and similar to 300.5(B), draws
attention to the inside of all raceways and enclosures installed in an
abovegrade wet location. The inside of these raceways and enclosures now
definitively requires conductors and cables suitable for use in wet
locations in accordance with to 310.8." - Explanatory note

 

310.8 Locations.

(C) Wet Locations. Insulated conductors and cables used in wet locations
shall comply with one of the following:     

(1)          Be moisture-impervious metal-sheathed 

(2)          Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THWN, THWN-2,
XHHW, XHHW-2, ZW 

(3)          Be of a type listed for use in wet locations

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Friday, October 26, 2012 2:03 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase and Romex

 

Glenn/Jason,

So you wouldn't use romex to feed an exterior outlet on an outside wall, or
to any outside lights???

 

Canadian Electrical Code's (CE Code) definitions.

wet location -a location in which liquids may drip, splash, or flow on or
against electrical equipment.

Damp location -an exterior or interior location that is normally or
periodically subject to condensation of moisture in, on, or, adjacent to
electrical equipment an includes partially protected locations under
canopies, parquees, roofed open porches, and similar locations.

Dry location -a location not normally subject to dampness, but that may
include a location subject to temporary dampness as in the case of a
building under construction, provided that ventilation is adequate to
prevent an accumulation of moisture. 

 

If inside your attic is considered a "wet location", then you have other
issues.  Are you sure the NEC's definition of 'wet location' is relating to
the location of the romex?

I just spoke to one of my inspectors and he sees no issue with entering the
bottom of a soladeck with romex.  

 

On the grounding/bonding, I have been using the bare wire in the romex for
the enphase system ground (within the enphase cable) and running a #6 from
the mod frames and rails into the soladeck and along side the romex back to
the panelboard.

 

I need to get myself a copy of your NEC so I can be on the same page as you
guys.  I hear it is written in a way that is much easier to interpret than
the CE Code, which is written in a very legal jargon.

 

Cheers,

benn

DayStar Renewable Energy Inc. 

www.daystarsolar.ca  *  Ph: 780-906-7807 

Construction Electrician Solar Photovoltaic Systems Certified

Certificate # 0007S

HAVE A SUNNY DAY

 

On 25/10/12 9:37 AM, "Glenn Burt" <glenn.burt at glbcc.com> wrote:

 

Soladeck on the rooftop places it in an environment that is considered
'wet'.

I don't think Romex is listed for use in a wet environment.

 

This would force you to use the proposed jbox in the attic for the
transition location.

I also understood that you could combine the EGC and GEC into a single
conductor as long as it is continuous or irreversibly spliced, as part of
the '08 code.

 

-Glenn Burt

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, October 25, 2012 9:13 AM
To: RE-wrenches
Subject: [RE-wrenches] Enphase and Romex

 

I'm sure this has been covered, but I could not find it in the archives.

 

We are considering using Romex in the attic for the first time. My plan was
to use the new Enphase coupler to connect the trunk cable to Type TC-ER,
enter a Soladeck passthrough box on the roof into a junction box in the
attic where I would make the transition to 10/3 Romex. I'm hung up on the
GEC going back to the service panel. Any suggestions?

 

By the way, we are on NEC 2008, and in most cases there is also a
requirement for an additional grounding electrode per NEC 690.47(D) (that
shouldn't really relate to my issue).

Jason Szumlanski 

Fafco Solar

_______________________________________________ List sponsored by Home Power
magazine List Address: RE-wrenches at lists.re-wrenches.org Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant
bios: www.members.re-wrenches.org 






_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121031/4c7dc7d6/attachment-0004.html>


More information about the RE-wrenches mailing list