Jason, 
Why don't you transition to romex in the Soladeck, eliminating the need for a junction box in the attic?

I abide by the CE Code (Canadian) and run a #6green from the roof to the dist pnl. 

benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and typos. 

On 2012-10-25, at 7:12 AM, Jason Szumlanski <jason at fafcosolar.com> wrote:

> I'm sure this has been covered, but I could not find it in the archives.
> 
> We are considering using Romex in the attic for the first time. My plan was to use the new Enphase coupler to connect the trunk cable to Type TC-ER, enter a Soladeck passthrough box on the roof into a junction box in the attic where I would make the transition to 10/3 Romex. I'm hung up on the GEC going back to the service panel. Any suggestions?
> 
> By the way, we are on NEC 2008, and in most cases there is also a requirement for an additional grounding electrode per NEC 690.47(D) (that shouldn't really relate to my issue).
> 
> Jason Szumlanski 
> Fafco Solar
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121025/0ee161c6/attachment-0004.html>


More information about the RE-wrenches mailing list