[RE-wrenches] Trojan 2 volt L-16s
Kirk Herander
kirk at vtsolar.com
Mon Oct 8 13:41:51 PDT 2012
The Rolls L16 series 2 vdc are single cells. They come in three AH
capacities @ C20, the S-1590 being 1200 ahr. I will say I have not good luck
with the lowest capacity S-1380(1050 ahr). Won't hold a charge after only 1
yr in service at recommended charge rate.
Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John
DeBoever
Sent: Monday, October 08, 2012 4:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan 2 volt L-16s
William, Wrenches,
Thank you for asking.
Indeed the Trojan Premium L16RE-2V is a monoblock flooded lead-acid
battery. The cells inside the monoblock are configured in parallel with
internal interconnects that are factory-welded and typically offer lower
resistance disparity compared to external interconnect cables and hardware
connections. This typically results in slower promotion of uneven cells
typical in battery banks. Let's look at an example, when selecting an L16 2V
version vs. a L16 6V version of for the same battery bank Ah capacity:
For example, let's compare:
o A battery bank of 1,110 Ah @ C20 @ 24V, configured as one string
consisting of 12x L16RE-2V
= total of 12x L16RE-2V
= one string, thus total charging current (Icharger) goes through all the
external interconnects cables of the string
= Icharger = I1 = I2 = I3, same current, most likely will age the units on
a most similar way, with less impact on promoting uneven cells over time,
although still possible.
With
o A battery bank of 1,110 Ah @ C20 @ 24V, configured as 3 strings in
parallel, each strings consisting of 4x L16RE-B
= total of 12x L16RE-B
= three strings in parallel, thus total charging current (Icharger= I1 + I2
+ I3) is divided into theoretically three same current in each string,
except there is a higher probability that each string resistance will differ
faster over time, thus promoting faster uneven cells
For memo, Trojan IND line are true 2V single cells, configured as 2V, or,
4V or 6V bundles in series in a dual-container. These 2V single cells will
be perfect to consider for larger Ah battery banks.
Sunniest regards,
John
John F. DeBoever
Global Technical & Projects Director - Renewable Energy
Trojan Battery Company
12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboever at trojanbattery.com
www.trojanbattery.com
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, October 08, 2012 2:59 PM
To: RE-wrenches
Subject: [RE-wrenches] Trojan 2 volt L-16s
Friends:
Has anyone used the Trojan 2 volt L-16 batteries? They each have 3 cells, I
presume in parallel.
The question presents: Although you can divide the strings by three, there
are still an equal number of batteries and cells to maintain and to get out
of whack. Will these batteries be equally likely or less likely to have
cell imbalances in the future?
The only benefit I see is a reduction in string wiring jumpers.
Comments?
Thanks in advance.
William Miller
Miller Solar
Voice :805-438-5600
email: <mailto:william at millersolar.com> william at millersolar.com
<http://millersolar.com> http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: <mailto:RE-wrenches at lists.re-wrenches.org>
RE-wrenches at lists.re-wrenches.org
Options & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm
Check out participant bios:
<http://www.members.re-wrenches.org> www.members.re-wrenches.org
This e-mail message and any attachments that accompany it may contain
information that is confidential, privileged, or protected from disclosure.
It is intended solely for the use of the individual(s) to whom it was
intended to be addressed. If you have received this e-mail by mistake, or
you are not the intended recipient, any reading, disclosure, copying or
other use of this communication is strictly prohibited. If you have received
this communication in error, please immediately advise the sender at their
phone number listed above, or by electronic mail, and also permanently
delete the original and all copies of this e-mail and any attachments from
all locations. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121008/c974f3d7/attachment-0004.html>
More information about the RE-wrenches
mailing list