[RE-wrenches] 120% rule applying to conductors
William Miller
william at millersolar.com
Fri Sep 28 08:25:25 PDT 2012
Friends:
Keep in mind that Mac asked us about application of a specific section of
the NEC, not if the rule makes any sense.
William Miller
At 05:32 AM 9/28/2012, you wrote:
>Are you sure you can't? Since the bus has a rating of 150 A and is
>protected by a 100 A breaker, there is plenty of room to not over amp the
>bus from the two sources of power.
>
>The amperage from the inverter will cancel amperage coming from the
>utility in the feeder. The wire will never supply over the 100 A. The
>theoretical max the inverter could backfeed would be 40 Amps in the 100
>Amp cable if no loads were being supplied. It would certainly not be a
>safety issue. Am I missing something in the code?