[RE-wrenches] 120% rule applying to conductors
Nick Vida
nickvida at ymail.com
Thu Sep 27 22:56:17 PDT 2012
What size is the conduit? Can you re-pull conductors at a higher ampacity?
Nick Vida
Mac: Nope. William Miller PS: It's pretty straight forwards, the code says "bus or conductor." wm PPS: Can you customer live with a smaller feeder breaker, say 125 amps? If so,
your gold. wm At 06:43 PM 9/27/2012, you wrote:
>Hello wrenches, >>I am looking for advice on how the 120% rule applies to feeders for a >subpanel. I have this scenario: >150A bus rating on subpanel with main breaker of 100A. The conductors >feeding this subpanel are 100A rated conductors. Can I backfeed with a >40A breaker? >>Thanks