[RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?
Drake
drake.chamberlin at redwoodalliance.org
Sat Sep 15 05:26:41 PDT 2012
This is from the 2008 NEC
690.13 All Conductors.
Means shall be provided to disconnect all current-carrying conductors
of a photovoltaic power source from all other conductors in a
building or other structure. A switch, circuit breaker, or other
device, either ac or dc, shall not be installed in a grounded
conductor if operation of that switch, circuit breaker, or other
device leaves the marked, grounded conductor in an ungrounded and
energized state.
Exception: A switch or circuit breaker that is part of a
ground-fault detection system required by 690.5 shall be permitted to
open the grounded conductor when that switch or circuit breaker is
automatically opened as a normal function of the device in responding
to ground faults. The switch or circuit breaker shall indicate the
presence of a ground fault.
FPN: The grounded conductor may have a bolted or terminal
disconnecting means to allow maintenance or troubleshooting by
qualified personnel.
At 04:51 AM 9/15/2012, you wrote:
>>Bob,
>
>The problem with switching both conductors (in a normally grounded
>array) is that opening the disconnect removes the bond to ground.
>This takes the ground fault protection and detection system out of
>the scheme (which would at least have operated with the disconnect
>open on the normally ungrounded conductor).
>
>An inspector should appreciate the value of maintaining the
>functionality of the ground fault protection system. 690.13 makes
>this clear, by allowing the grounded conductor to be disconnected by
>service personnel.
>
>Isaac Opalinsky
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
More information about the RE-wrenches
mailing list