[RE-wrenches] Up for a 1-Line Riddle?
David Brearley
david.brearley at solarprofessional.com
Thu Aug 30 14:26:36 PDT 2012
Yeah, that threw me at first, too. Especially since at 240 V, the ac output of that inverter is 21 A, which is half of the reported 42 A phase current.
On Aug 30, 2012, at 3:56 PM, Dave Click wrote:
> Thanks David, I was in residential mode and just saw the 240V listed in the OCPD table!
>
> On 2012/8/30 16:47, David Brearley wrote:
>> I'm assuming it's a balanced 3-phase interconnection, which fits with the reported phase current of 42 A:
>>
>> (3 x 5000 W) / 208 V / 1.73 = 41.7 A
>>
>> Or more simply:
>>
>> 24 A per inverter x 1.73 = 41.5 A
>>
>> However, no one reviewing a single-line should have to guess about the service type....
>>
>> On Aug 30, 2012, at 3:12 PM, Dave Click wrote:
>>
>>> I've seen that one a lot, too. And not to quibble, but the 1-line depicts this correctly (no inline fuse shown in the inverter DC disconnect box), though there should be a note making this more explicit.
>>>
>>> Speaking of sunny days turning off the system, how about the 3 30A inverter breakers' combined feed going into a 55A breaker. Also... a 55A breaker? Really? I guess the designer wanted to leave a little headroom to avoid scaring the 60A disconnect.
>>>
>>> DKC
>>>
>>> On 2012/8/30 14:35, Andrew Truitt wrote:
>>>>
>>>> Ahh yes, the old "combine strings before landing on a fused DC input
>>>> terminal" trick. Sure to blow the fuse the first sunny day. This is
>>>> why SMA created their fuse-bypass DC input terminal. I take it the
>>>> installer was not aware of this...
>>>>
>>>>
>>>>
>>>> For a brighter energy future,
>>>>
>>>>
>>>> Andrew Truitt
>>>> NABCEP Certified PV Installer™ (ID# 032407-66)____
>>>>
>>>> Principal
>>>> Truitt Renewable Energy Consulting____
>>>>
>>>> (202) 486-7507 <tel:%28202%29%20486-7507>____
>>>>
>>>> http://www.linkedin.com/pub/andrew-truitt/8/622/713
>>>>
>>>>
>>>>
>>>> "Don't get me wrong: I love nuclear energy! It's just that I prefer
>>>> fusion to fission. And it just so happens that there's an enormous
>>>> fusion reactor safely banked a few million miles from us. It delivers
>>>> more than we could ever use in just about 8 minutes. And it's wireless!"
>>>>
>>>> ~William McDonough
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski <jason at fafcosolar.com
>>>> <mailto:jason at fafcosolar.com>> wrote:
>>>>
>>>> I was sent to look at another contractor's work, and found three
>>>> SB5000 inverters with blown string input fuses. I was able to
>>>> determine the reason pretty quickly, and was later sent the original
>>>> 1-Line, which was installed per the drawings. The 1-Line came from a
>>>> "leading system integrator" who shall remain nameless.
>>>>
>>>> See anything wrong?
>>>>
>>>> https://www.sugarsync.com/pf/D6539806_8669786_010829
>>>>
>>>> Just goes to show you - the contractor needs to take responsibility
>>>> and verify the specifications are correct, safe, and code compliant.
>>>>
>>>> Jason Szumlanski
>>>> Fafco Solar
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list