[RE-wrenches] Disconnets

Ryan Mayfield ryan at renewableassociates.com
Mon Aug 27 15:06:48 PDT 2012


Jesse,


You may want to check out the new(ish) line from GE and Eaton. Both have
600VDC listings, Eaton's newer line has 3 and 6 pole versions available. I
have the Eaton disconnects specified for an upcoming job but I haven't used
either as of yet.

 

http://www.geindustrial.com/cwc/Dispatcher?REQUEST=PRODUCTS
<http://www.geindustrial.com/cwc/Dispatcher?REQUEST=PRODUCTS&pnlid=5&famid=3
9&catid=62&id=Solar-SD> &pnlid=5&famid=39&catid=62&id=Solar-SD

http://www.eaton.com/Eaton/ProductsServices/Electrical/ProductsandServices/E
lectricalDistribution/SwitchesandDisconnects/SolarDisconnects/index.htm 


Ryan

 

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Friday, August 24, 2012 6:43 PM
To: RE-wrenches
Subject: [RE-wrenches] Disconnets

 

Hello,

 

I've been having a long conversation with a local guy about disconnects that
are usable in DC PV circuits.  From what I have seen, GE, Eaton... they are
usable up to the 250VDC it has listed on the labels, or more if poles are
wired in series. The squared D 600Vac/dc is self tested to 600VDC/pole.  The
disconnects in question are not the "solar disconnects" on the market now. 

 

What are people using for the GDI systems?  I seem to think that if if says
250VDC on the label, that is its rating unless you wire pole in series and
the manufacturer has literature saying that that is acceptable.  

 

Thoughts on the square D self listing?

 

 

Jesse

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120827/acf8f865/attachment-0004.html>


More information about the RE-wrenches mailing list