I really don't think there is a problem using the SQD if you can series up a
couple of poles.
-Glenn
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Friday, August 24, 2012 9:43 PM
To: RE-wrenches
Subject: [RE-wrenches] Disconnets
Hello,
I've been having a long conversation with a local guy about disconnects that
are usable in DC PV circuits. From what I have seen, GE, Eaton... they are
usable up to the 250VDC it has listed on the labels, or more if poles are
wired in series. The squared D 600Vac/dc is self tested to 600VDC/pole. The
disconnects in question are not the "solar disconnects" on the market now.
What are people using for the GDI systems? I seem to think that if if says
250VDC on the label, that is its rating unless you wire pole in series and
the manufacturer has literature saying that that is acceptable.
Thoughts on the square D self listing?
Jesse