I always thought that installing lag screws was tough enough with pilot 
holes- I should hit the gym. I'm not a structural PE, but I think that 
not drilling pilot holes violates the American Wood Council's National 
Design Specs and therefore violates the IBC too. I would imagine that 
you'd be much more likely to split your trusses. IBC also requires 
flashings be used but at least around here inspectors never ask for it 
(which makes sense- as you all know, Florida never sees wind or rain, 
and definitely not at the same time). What silicone do you use that's 
compatible with asphalt shingles?

DKC

On 2012/7/1 21:13, mark at hurshtown.com wrote:
> In my 20 year experience of lagging down L feet on shingle roofs in
> Indiana with a good dollop of silicone caulk under the foot, I've never
> had an issue. No pre-drilling, just drive the lag home. Drilling a hole
> first is not necessary, and reduces holding strength. No reason to make
> a science project out of it and increase cost and labor.
>
> Mark
>
>     -------- Original Message --------
>     Subject: Re: [RE-wrenches] L feet no flashing in shingle roof
>     From: Drake <drake.chamberlin at redwoodalliance.org
>     <mailto:drake.chamberlin at redwoodalliance.org>>
>     Date: Fri, June 29, 2012 3:09 pm
>     To: RE-wrenches <re-wrenches at lists.re-wrenches.org
>     <mailto:re-wrenches at lists.re-wrenches.org>>
>
>     Hi Jay,
>
>     There is no room for flashings. The L feet will go very close to the
>     skylights and the flashing would hit the edge of them. Plus there is
>     an existing array that was done by another installer that is done
>     with L feet only. The new array would be higher.
>
>
>>     And given that we have really good off the shelf approved flashed
>>     feet, why would you use anything else?
>>
>>     My 2 cents,
>>
>>     Jay
>>
>>     peltz power
>>
>>
>>     On Jun 29, 2012, at 5:16 AM, Glenn Burt wrote:
>>
>>>     We have used a variety of sealants over the years, and determined
>>>     simple Henry roofing cement is the best product for use on comp
>>>     roofing.
>>>
>>>     We also used to bend our own L-foot flashing, which we cut from
>>>     standard Al coil stock (before all the manufactured options were
>>>     available). This might be a good option for you in this case.
>>>
>>>
>>>
>>>     Glenn
>>>
>>>     *From:* re-wrenches-bounces at lists.re-wrenches.org
>>>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>
>>>     [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>>>     *Drake
>>>     *Sent:* Thursday, June 28, 2012 6:40 PM
>>>     *To:* RE-wrenches
>>>     *Subject:* [RE-wrenches] L feet no flashing in shingle roof
>>>
>>>     I'm quoting a job that has an existing array with L feet bolted
>>>     down to a shingle roof with no flashings. I want to match the
>>>     height of the existing array. Also some modules are being worked
>>>     in around skylights where it is unlikely that room would be
>>>     available for flashings to center over rafters.
>>>
>>>     I've always used flashings. Would it be completely crazy to
>>>     follow suit of the existing array and bolt L feet straight to the
>>>     shingle roof with good roof sealant? If so, how would you seal it?
>     Drake Chamberlin
>     ATHENS ELECTRIC LLC
>     OH License 44810
>     CO license 3773
>     NABCEP Certified PV
>     ------------------------------------------------------------------------
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>



More information about the RE-wrenches mailing list