Wed Jun 27 18:01:33 PDT 2012
Bill:
This scenario is not NEC compliant. The inverter feeds need to connect to
a dedicated OC device only, not additional loads. 690.64(B)
William Miller
At 01:22 PM 6/27/2012, you wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_0238_01CD5478.B9201A70"
>Content-Language: en-us
>
>We are doing a tracking system and need to run a couple conductors back
>out from the house to power the tracker. I suggested that we tap off of
>the output from one of the AC legs of the Enphase output instead. From the
>inventor of the tracker: from the manufacturer"The tracker needs 12V 10A
>on demand. I have found that a small battery w/ charger nearby or AC to DC
>converter to 20A (for surge) will work." These would be short surges of
>perhaps 4 seconds. Since it is backfeeding onto the lines instead of
>powering a device, i.e. a motor which might overheat if there is an
>imbalance, the only consideration would seem to be that the frequency of
>the signal remain stable. Once in the bus bar of the house panel, it would
>be irrelevant that there would be a temporary voltage drop or slight imbalance.
>
>Any thoughts? Thank you.