I think that technically, the combiner panel is not compliant if the 
possible feeds from various sources exceed 120% of the busbar rating.

Inspectors have been reasonable on this issue, as it can be done 
safely.  The solution, if the AHJ won't accept a small combiner panel 
is to use a panel with a higher busbar rating and a main breaker 
small enough so that the combination of the main and solar feeds does 
not exceed 120% of the busbar rating.  It can result in some 
awkwardly large and technically unnecessary boxes.


At 07:29 AM 6/27/2012, you wrote:
>If the combining panel is next to the main panel, can you use a Main 
>Lug panel as the combining panel or does it need a main breaker? I'm 
>not sure what the purpose of the main breaker would be if there are no loads.
>
>--
>Chris Mason
>President, Comet Systems Ltd
><http://www.cometenergysystems.com>www.cometenergysystems.com
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org

Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120627/7fd73ddb/attachment-0004.html>


More information about the RE-wrenches mailing list