[RE-wrenches] PV into a resistor: please advise

boB at midnitesolar.com boB at midnitesolar.com
Sun May 20 11:19:36 PDT 2012


On 5/20/2012 7:20 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
> boB,
> I know I'm getting out of my league here but I'm so intrigued. Doesn't 
> a LCB device work on a feedback loop that looks at the output voltage 
> and current to a load and compares it to input voltage? Since we have 
> two fixed values here, 29? resistance and 4.15A PV current, how can 
> there be any excess voltage at the circuit input?
>
> I can see that the PV modules should produce 1kW @ 500W/m2 IF the load 
> allowed it. As Kent said, the resistance would have to change to 
> 58?. On the other hand...if I don't understand the function of a 
> LCB...operating the PV module at 170 Vdc would result in 5.87 amps 
> while feeding a 29? load.
>
> Counterpoint? Inquiring minds want to know!


I don't know exactly how they work either...   There was not quite 
enough depth on the web site I went to.

It just seemed sorta (to me) like what I described...  An MPPT without 
batteries running on the input (PV) side.
i.e. Higher input voltage at a lower current transforms into lower 
voltage at higher current at the output side.

I did find some supposed' LCB schematics  online that were pretty much 
was what I expected.

To get max current and therefore max power across an output resistive 
load, the input voltage must be
at MPP voltage of the PV which (to me) means it would have to be an MPPT 
type device. Without a
battery, the output voltage would not matter so I think of it as a

Another use for a circuit like this would be a cathodic protection device.

So, if that is the case, it could be correct as is, OR, may be with SMOP 
(Simple Matter Of Programming) which isn't
necessarily all that simple.  Looks like the voltage that Mick is 
looking for may be too high for the application
he is wanting though.

Please let me know if I'm wrong here as I'd love to know.

boB





>
>
>
>
> On May 19, 2012, at 10:16 PM, boB at midnitesolar.com 
> <mailto:boB at midnitesolar.com> wrote:
>
> On 5/19/2012 5:47 PM, Larry Crutcher, Starlight Solar Power Systems 
> wrote:
>> Good one, Mick. Here's the way I see it:
>>
>> For question one, I say yes, other than the obvious wire and 
>> connection losses, because you are operating the cell(s) at the peak 
>> power point.
>>
>> Since a PV solar cell is a constant current device and your 29 ohm 
>> load did not change, reducing your Lab Light source to 500 W/m2 can 
>> only affect the voltage and resulting power. This means your load 
>> forces the voltage down to 120 volts resulting in 500 watts of power 
>> dissipated. You have forced an IV curve shift of current AND voltage.
>>
>> The LCB boosts current based on IV curve voltage. I don't think an 
>> LCB can change anything in this scenario since you have forced the 
>> circuit to operate at 120 volts and 4.15 amps.
>
>
>
> Realizing that these LCB things run off the PV input because there is 
> no battery....  If an LCB outputs
> maximum current into a fixed resistance, (and therefore maximum 
> power), kind of like an MPPT
> charge controller does,  then it ~should~  adjust its  voltage "gear 
> ratio" to maximize the output
> current and power.
>
> At least I think the idea is correct, if the LCB was large enough and 
> high enough voltage operation
> for your application.     But then again, I may be missing something 
> here too.
>
>
> boB
>
>
>>
>> Keep in mind that I'm a solar dummy. My logic may be faulty.
>>
>> Larry Crutcher
>> Starlight Solar Power Systems
>> (928) 342-9103
>> _www.starlightsolar.com <http://www.starlightsolar.com/>_
>> _
>> _
>> _
>> _
>>
>>
>> On May 19, 2012, at 12:35 PM, Mick Abraham wrote:
>>
>> Hi, Wrenchies~
>> Kindly educate me regarding PV behavior when the load is a resistor. 
>> Here's a hypothetical situation:
>> * Eight 250 watt PV modules (60 cells per module), all connected in 
>> series for "peak" ratings of 240 volts DC & 8.3 amps
>> * Lab type cell temperature & illumination so that the eight would 
>> truly pump 2,000 watts */into an ideal load/*
>> * A 240 volt AC heating element designed for 2,000 watt heat 
>> dissipation at 240 volts AC...that's about 29 ohms resistance for the 
>> heat element
>> * Connect the PV string to the heat element, with nothing in 
>> between except a fused disconnect.
>> In the above situation, would the resistance of the heating element 
>> be all that's needed to force the PV array to operate near the "peak" 
>> wattage?
>> Would the heater actually get 2,000 watts to turn into heat?
>> +++++++++++++++++++++++++++
>> Now consider the same cell temperature but half the illumination. 
>> That's similar voltage but half the amps at peak wattage. If this is 
>> sent into the same 29 ohm
>> resistor--again with no intervening electronics, could we count on 
>> 1000 watts of heat?
>> If the answers come up "no", would the power throughput be helped 
>> by a SolarConverters style MPPT pump controller (Linear Current 
>> Booster kinda thing), assuming that one could be found to operate in 
>> the 240 volt range?
>> Thanks & Jolliness,
>>
>> Mick Abraham, Proprietor
>> www.abrahamsolar.com <http://www.abrahamsolar.com/>
>>
>>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120520/586f12e3/attachment-0004.html>


More information about the RE-wrenches mailing list